Absolutely, but thats not what Im saying. If they are extraneous, which is what im being led to believe they are, then they must be supp bonded. My arguement then is that the only way to tell if they are bonded to start with is is to see if the bonding is physically there! It doesnt mean its complete, it could be broken. But if it is there then testing confirms the adequacy of said bonding, not that the bonding is there in the first place.
Ideally you're right, but with periodic inspection we are not dealing with ideals, we're dealing with limitations.
No, if doing an EICR you do it to the latest regulations and record your deviances as such -- no bonding is a deviation-- you dont inspect to what previous regs may have allowed or not. What you have is an caveat in the regs that because it was to a previous reg it doesnt make it unsafe, you as the inspector make that call. (I'm not that old but hasnt supp bonding always been a requirement under previous regs??). My arguement is that the "governing bodies" have deemed it unsafe not to have it without RCD top cover but whether you hold to this is entirely your choice as the inspector. Only you answer for your decisions on how you code it!
You misunderstand me. I wasn't referring to a 'new' installation in terms of its compliance with current regs, I was referring to a new installation in general. If you were wiring from scratch and supplementary bonding was needed then you'd
have to fit it and then test it to confirm its effectiveness, but when carrying out periodic inspection then you are making assumptions as to its suitability for continued use. If a test indicates that supplementary bonding is there or is as good as there then you can assume that it is.
Wrong, you seriously believe additional protection is not for fault protection?. (Check 415.2 note 1). If not for fault what do you actually believe it is there for?
No, it is an
addition to fault protection, it is not used
for fault protection. See 415.2 note 2.
If you cant disconnect all other bonding (cos you dont know what other bonding may be hidden?) the only failsure method to prove supp may be there is to see it.
I agree
To prove it is effective you test
I agree
not the other way around.
I agree, with a 'but'.
Thats my arguement, the equation is flawed unless you have disconnect all other bonding as you will get a reading and assume it is present even if it isnt?
Your right though, I wont be ripping up floor boards. If I cant see any signs of supp bonding I assume its not there and code -- I wont rely on a test between part to prove supp bonding is present.
But you rely on an R1+R2 test to prove that a cpc is there don't you??? No. Think about it, unless you are carrying out initial verification there is not a single continuity test you can carry out without risk of parallel paths being present. You are carrying out an EICR, you are not there to 'prove' anything, you can however use your test results to
suggest that it is there.
Valid point, you could exclude from the EICR. Personally I wont.
I wouldn't exclude, I would say that although I cannot see any sign of supplementary bonding, my test results suggest that it is there.
Not necesarily, if you have parallel paths due to other bonding elsewhere in the premises you will always get a reading. Only if you can remove every possible parallel path would this method be effective. (Have I just convinced myself of a possible method to use this for proving the presence of supp bonding?)
As above, do you ensure the removal of every parallel path when conducting an R1+R2 test during an EICR?
And what do you believe additional protection is for if not to protect against a fault?
As above, it is in addition to...
I'll leave that one with you to argue! I in no way consider myself of sufficient knowledge and experience to challenge the 'big boys' and their technical 'experts' -- plus on their interpretation and guidance I actually think they are right!
Big boys??? No mate, suits, nothing more, many of which with little experience of the practical application of the regulations. Could I challenge them on the whole regs book? No, certainly not. But I could certainly challenge them on certain sections!
In agreement with you there if the evidence supports the probability. But my disagreement on this particualr issue with supp bonding is that not being able to see it I wont rely on a test to convince me (evidence) that it is there. I am risk adverse, numerous kickings for assumptions at work have made me that way, so always err on the side of caution. The receiver of the EICR can ignore what I state if they want, its my perogative as the inspector to make my assessment and its the perogative of the client to ignore it. I just like knowing my butt is covered should the sh8t hit the fan!
Again, when carrying out an EICR you're working with what you have and what you can see and test. It is a report, not a certificate, therefore you can say whatever you want really! If you wanted to give everything a C1 regardless of its severity then that's your prerogative (although evidently you wouldn't make a very good inspector), and you still remain responsible for nowt! Every inspection you carry out and every test result you gain is nothing more than a suggestion as to the current safety of the installation. I reiterate, periodic inspection and initial verification are two completely different ball games.
p.s. I have no personal disagreement with anyone, im just exploring the technicalities of supp bonding
Neither do I, but the vagueness of the regulations gives rise to threads such as this occuring highlighting the relevance of my comment regarding challenging the suits up at the IET!