Yep C2 is what i have always attributed to a situation like this.....
Good, you've not gone over to the 'dark' side then!
(Comment passed whilst sat on the boundary watching the match with a beer)
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss EICR and Supplementary Bonding. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Yep C2 is what i have always attributed to a situation like this.....
Biff may I point you to this part (high-lighted in the text), which was the guidance issued by the ESC, albeit not in the BGB.
This was in the older version of the BP guides, I will have a look and see if it is in a newer version.
415.2.2
Where doubt exists regarding the effectiveness of supplementary equipotential bonding, it shall be confirmed that the resistance R between simultaneously accessible exposed-conductive parts and extraneous conductive parts fulfils the following criteria:
R< or = to 50V/Ia in AC systems
Where Ia is the operating current in amperes of the protective device - for over current devices the current causing the automatic operation in 5s.
see above, that's exactly what BS7671:2008 states, if this has changed in the update then fair enough, but I'm not aware of that change... sure someone who hasn't had the BGB nicked by their spark will confirm it one way or the other.unless someones trying to suggest , in the complete absence of any official guidance whatsoever , is that once supp. bonding cant be visually confirmed , that the inspectors next step is to start randomly carrying continuity tests between bits of metal in the bathroom , in the hope that good readings can now justify a defect reduction to C3 ??
get real.
;-)
see above, that's exactly what BS7671:2008 states, if this has changed in the update then fair enough, but I'm not aware of that change... sure someone who hasn't had the BGB nicked by their spark will confirm it one way or the other.
Biff may I point you to this part (high-lighted in the text)
Note: where the presence of supplementarybonding cannot be confirmed by inspection, it
may be verified by a continuity test ** (< 0.05 ohm) **
Between pipework and metal light carcass **0.44ohms
Between pipework and downflow heater circuit cpc** ​0.26ohms.
cheers, so what's the chances of this now being settled then?Still in the BGB mate.
Supplementary bonding shall be provided by a supplementary conductor, a conductive part of a permanent and reliable nature, or by a combination of these.
.... so what's the chances of this now being settled then? ......