Hi hope every one is having a good weekend.

I have recently started a job with a can who do eicr's/foxed wire testing and as I have only been qualified 2 years and worked mainly in commercial new installation so I have not had much experian in domestic eicr's. They are starting to train me by going around with the boss to the jobs but he has given me some examples and asked what I would do and one of them was "you go to a house and there is a plastic consumer unit with mcb's but has no rcd protection, the cables are buried into the walls" I think I would recommend a board change as the cables buried into the walls will probily be less than 50mm and also if I remember correctly in amendment 3 all cables going through the bathroom need rcd protection so would recommend a board change. Not that it will definatly need it as just because it is not not comply with current regs does not mean it is unsafe that's why it is recommended.

I could be totally wrong but that's why I am asking. If i am totally wrong can I ask what you would recommend a board change for?
 
It's not your place as an inspector to make recommendations. It's your place to make observations. That is all. The only recommendation made in connection to an observation is the level of urgency required to rectify the issue that has been noted and coded appropriately. Such recommendations are already set in stone.

If you are later approached to remedy observations made, there are many ways to skin a cat.

If all you're entering into the periodic inspection game for is to consistently recommend board changes, you're kidding yourself that you're a professional.
 
Last edited:
It is for a local authority and was told by my new boss that it has to be satisfactory they won't accept any thing else so if it needs stuff to make it satisfactory then it gets done, that's why I'm asking as if I do a c1 or c2 it needs to be sorted that includes missing bonding (as long as it needs it) or boards like if there is a whole in the board casing or stuff like that. That is why I am asking.

Also I am only entering into this because i it's the job I got as it is better than no job but I don't want to work in domestic or doing eicr's but that's the job I have.

I don't intend to just recommend board changes at all I'm just trying to see what would make you all think a board needed replacing
 
After a client has approached me to rectify issues brought to light in an EICR, I would recommend a board change if it was the cheapest and simplest way to rectify a C2 or a number of C2s. There would also be a suggestion that the introduction of RCDs will improve the safety of the installation but the client would be made fully aware that there is no requirement for them to do so.

For example; remember that a lack of RCD protected circuits in a bathroom is still only a C3. If however there is no RCD protection then it would be a lack of supplementary bonding within that same bathroom that would be a C2.

Would I recommend a ÂŁ500 board change if all it would cost is ÂŁ150 to bring the supplementary bonding up to standards? Most probably not.

Like I said, there are many ways to skin a cat, and as long as you are open and transparent with clients with regards to your methods, you cant go far wrong.
 
I totally agree that the cheapest way is better for the client and 150 sup bonding is cheaper than a board change.

Can I ask how long you would normally get to do a eicr in a standard 2 bed house with about 7 or 8 circuits?

I don't think the tests are to generate business well Not that I am aware of, I only started on Friday and shadowed one of there electricians and he basically walked into a house looked at the board and saw no rcd protection and walked out and put on the report that board change is required for rcd protection and that there is no reason to test as it would be tested when the board is changed which I thought was wrong but as I never done one was not sure. That is why I am going with the boss next week to see what is needed. I'm hoping he isn't just trying to make reasons to get remedials but I don't know as of yet
 
I totally agree that the cheapest way is better for the client and 150 sup bonding is cheaper than a board change.

Can I ask how long you would normally get to do a eicr in a standard 2 bed house with about 7 or 8 circuits?

I don't think the tests are to generate business well Not that I am aware of, I only started on Friday and shadowed one of there electricians and he basically walked into a house looked at the board and saw no rcd protection and walked out and put on the report that board change is required for rcd protection and that there is no reason to test as it would be tested when the board is changed which I thought was wrong but as I never done one was not sure. That is why I am going with the boss next week to see what is needed. I'm hoping he isn't just trying to make reasons to get remedials but I don't know as of yet

The report is "precisely" to generate business.

A proper EICR, should be conducted on the installation... walking in, seeing no RCD and walking out is not a good sign.

Where did he tie up his horse?
 
After a client has approached me to rectify issues brought to light in an EICR, I would recommend a board change if it was the cheapest and simplest way to rectify a C2 or a number of C2s. There would also be a suggestion that the introduction of RCDs will improve the safety of the installation but the client would be made fully aware that there is no requirement for them to do so.

For example; remember that a lack of RCD protected circuits in a bathroom is still only a C3. If however there is no RCD protection then it would be a lack of supplementary bonding within that same bathroom that would be a C2.

Would I recommend a ÂŁ500 board change if all it would cost is ÂŁ150 to bring the supplementary bonding up to standards? Most probably not.

Like I said, there are many ways to skin a cat, and as long as you are open and transparent with clients with regards to your methods, you cant go far wrong.
welcome back, field marshall; where you been?
 
Can I ask how long you would normally get to do a eicr in a standard 2 bed house with about 7 or 8 circuits?

Four hours minimum, plus 30 minutes to write up at the end of the day.

I don't think the tests are to generate business well Not that I am aware of, I only started on Friday and shadowed one of there electricians and he basically walked into a house looked at the board and saw no rcd protection and walked out and put on the report that board change is required for rcd protection and that there is no reason to test as it would be tested when the board is changed which I thought was wrong but as I never done one was not sure. That is why I am going with the boss next week to see what is needed. I'm hoping he isn't just trying to make reasons to get remedials but I don't know as of yet

Think you need to find a new job fella. These people are nothing more than unscrupulous con men. Your boss is not an electrician.
 
There is a remote possibility the local authority has asked for this method of testing, no rcd, metal board etc.. to note it and move on but I doubt it. Get back into commercial work domestic is a rat race.
 
Hi every one just thought I would update you all the guy turned out to be a bit of rip off merchant, recommending board upgrades that was not needed even went so far as to say the board needed changing as it was damaged on a board he actually damaged trying to get the cover off (it had been painted round) as well as not even doing a proper eicr.

He told me that I needed to do 3-4 a day which included paperwork and the best way to do it was only live tests and to have a quick look around for damage that's it seemed a bit ---- to me when they was down as 100% fixed wire test.

So any way today I went and had a chat with him and quit which is ---- as now I'm out of work till I find something else but I didn't feel right doing what he asked me to.
 

Reply to Eicr, board change recommendation? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
395
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
980
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

The total current capacity of the system in amperes is the same as the per-phase rating when referring to a balanced three-phase system. Thus, a...
Replies
4
Views
665
S
  • Article
Low pressure mixer spray tap recommendations ? I'll be installing a new kitchen, DIY, and the Mrs wants a mixer tap with a switchable...
Replies
0
Views
172
Splitty
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top