Eicr bonding | Page 2 | on ElectriciansForums
Discuss Eicr bonding in the UK Electrical Forum area at ElectriciansForums.net
GarryJ
Ayrshire, Scotland
Evening all.
Just wondered what everyone's sequence was for inspecting/testing main bonding when carrying out EICRs?
I was at property recently and carried out a full 100% EICR. Everything was satisfactory and up to scratch - new 17th Ed split board / all circuits RCD protected there was a couple of code 3 items for no earth sleeving in pendants etc.
The property had both main water and gas services (TNC-S system) There was an isca block at the origin with 16mm earth going into consumer unit and 2 x 10mm earth cables disappearing under floor.
The main water stop cock according to the tennant was under the utility room floor and the gas box was on the side of the house but no bonding visible inside external box. (Main gas pipe also comes into property under floor.)
I classed these as a Code 2 and requiring further investigation. On front page of certificate I stated this in the agreed limitations stating it was unaccessible.
However since I was last there British gas has been in to provide gas safe certificate and can not do this as they also say they can not confirm main gas is bonded?
Thanks in advance for any help
Whereabouts in GN3 is it 'bandied about'?
There is a figure of 0.05 given as a suggested maximum value for the resistance between the cable termination at the bs951 clamp and the pipe itself.
good post. that 0.05 figure is misunderstood by so many sparks as being a max. value for the resistance of a main bonding conductor.
Garry,I think my approach would mirror tels post
The installation is of a good standard,the bonding cables exist at the consumer unit,the continuity test would ensure they were connected to the service they were intended for
Given the positives that you have stated I think it is a bit of over zealous to expect the installation to be considered potentially dangerous by coding it 2 but its your opinion that matters
[ElectriciansForums.net] Eicr bonding
Reply to Eicr bonding in the UK Electrical Forum area at ElectriciansForums.net
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
