Evening all.
Just wondered what everyone's sequence was for inspecting/testing main bonding when carrying out EICRs?
I was at property recently and carried out a full 100% EICR. Everything was satisfactory and up to scratch - new 17th Ed split board / all circuits RCD protected there was a couple of code 3 items for no earth sleeving in pendants etc.
The property had both main water and gas services (TNC-S system) There was an isca block at the origin with 16mm earth going into consumer unit and 2 x 10mm earth cables disappearing under floor.
The main water stop cock according to the tennant was under the utility room floor and the gas box was on the side of the house but no bonding visible inside external box. (Main gas pipe also comes into property under floor.)
I classed these as a Code 2 and requiring further investigation. On front page of certificate I stated this in the agreed limitations stating it was unaccessible.
However since I was last there British gas has been in to provide gas safe certificate and can not do this as they also say they can not confirm main gas is bonded?
Thanks in advance for any help
Just wondered what everyone's sequence was for inspecting/testing main bonding when carrying out EICRs?
I was at property recently and carried out a full 100% EICR. Everything was satisfactory and up to scratch - new 17th Ed split board / all circuits RCD protected there was a couple of code 3 items for no earth sleeving in pendants etc.
The property had both main water and gas services (TNC-S system) There was an isca block at the origin with 16mm earth going into consumer unit and 2 x 10mm earth cables disappearing under floor.
The main water stop cock according to the tennant was under the utility room floor and the gas box was on the side of the house but no bonding visible inside external box. (Main gas pipe also comes into property under floor.)
I classed these as a Code 2 and requiring further investigation. On front page of certificate I stated this in the agreed limitations stating it was unaccessible.
However since I was last there British gas has been in to provide gas safe certificate and can not do this as they also say they can not confirm main gas is bonded?
Thanks in advance for any help