Hi everyone,
Looking for honest opinions on C2 ratings on a recent EICR. Terrace house probably built 1930's, rented out. Not sure if this is a standard EICR template but text and C2 ratings for the following:
1. Consumer unit - manual operation of circuit breakers and RCD's to prove disconnection (643.10)
2. Presence of RCD six-monthly test noticeat or near consumer unit (514.12.2)
3. RCD(s) provided for fault protection - includes RCBOs (411.4.204, 411.5.2, 531.2)
4. RCD(s) provided for additional protection/requirements - includes RCBOs (411.3.3, 415.1)
5. Provision of additional requirements for protection by RCD not exceeding 30 mA
- for all socket outlets of rating 32A or less unless an exception is permitted (411.3.3)
- final circuits supplying luminaires within domestic (household) premises (411.3.4)
Overall comments are:
No visible earthing on living room lighting circuit (C2/FI)
Property currently has x 2 consumer units with no RCD protection (C2).
I've been reading around the subject and on this forum and these things seem to be open to interpretation. If the work needs done, I have no problem with that, just don't want to be ripped off for work that's not actually required!
Would be grateful for comments.
Thanks
Looking for honest opinions on C2 ratings on a recent EICR. Terrace house probably built 1930's, rented out. Not sure if this is a standard EICR template but text and C2 ratings for the following:
1. Consumer unit - manual operation of circuit breakers and RCD's to prove disconnection (643.10)
2. Presence of RCD six-monthly test noticeat or near consumer unit (514.12.2)
3. RCD(s) provided for fault protection - includes RCBOs (411.4.204, 411.5.2, 531.2)
4. RCD(s) provided for additional protection/requirements - includes RCBOs (411.3.3, 415.1)
5. Provision of additional requirements for protection by RCD not exceeding 30 mA
- for all socket outlets of rating 32A or less unless an exception is permitted (411.3.3)
- final circuits supplying luminaires within domestic (household) premises (411.3.4)
Overall comments are:
No visible earthing on living room lighting circuit (C2/FI)
Property currently has x 2 consumer units with no RCD protection (C2).
I've been reading around the subject and on this forum and these things seem to be open to interpretation. If the work needs done, I have no problem with that, just don't want to be ripped off for work that's not actually required!
Would be grateful for comments.
Thanks