EICR Code help | on ElectriciansForums
Discuss EICR Code help in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
stu75
Just tested a bungalow and fond the power is all supplied by one radial 2.5mm circuit rated at 32A on a fuse not MCB. Was thinking C2, there are only 15 points in the on the circuit and most re not used. will be carrying out a full rewire in a couple of weeks any way. If I reduce the fuse size to 20A con I get away with a C3?
If its a 2.5mm cable and the MCB is rated at 20A why would you code it at all?
The point of an EICR is to report the findings of the day - nothing more, nothing less. (EDIT: Unless you find a C1 you can fix on the spot IMHO)
2.5mm cable and a 30A BS 3036 is a C2 IMHO
Reply to EICR Code help in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
It isn't OK as it is otherwise it wouldn't have been coded C2 on an EICR.
davesparks
Definitely, although most likely within the accessories. I've often found that once accessories are disconnected the cabling IR is fine. Sometimes...