EICR Coding - Armour not glanded | Page 3 | on ElectriciansForums

Discuss EICR Coding - Armour not glanded in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

You need to make your own decision based on circumstances, BS7671 states a minimum C3 entry.
 
Just out of curiosity why would you give a non RCD'd circuit covering a Twin and earth buried cable as a C3?
is this not potential dangerous ?

C3 because it complied at the time of installation. just non-compliant with current regs.

I agree complete with with the sentiment that buried cables in prescribe cable zones are not that dangerous........ we have the Darwin awards for a reason!

Its complete subjective I don't think there a right or wrong answer.

But I have very few home owner's ask for an EICR, mainly when they're buying a house, and in that circumstance I would agree a C3,
and most like recommend a new CU for there Piece of there piece of mind.

Landlords and commercial customer asking for an EICR,

I would call it a C2, as these guys are doing this more for commercial, legal protection and insurance purpose, so in this instance cover your arse!

If its a landlord, he can spend the money and make the installation as safe as possible.

If its an employer, he can spend the money and make the installation as safe as possible.

If its a home owner, he can do what he like's. its very unlike he'll take me to court.
 
I went with the advice of FI in this instance, as I can't guarantee it's SWA but all evidence suggests it is. I'm no longer working for my uncle, I saved a copy of the report as I left it, so if he decides to change it to a C3 then that's on him, but I have the report showing exactly what I classified it as.

Left uncle on good terms, just want to cover my backside as you never know what's around the corner.
 
I agree with FI, I wired a HMO with SWA from Switch Fuse (Metal Wylex 110M) properly glanded in main intake cupboard to CU in flat. Terminating SWA on CU would be ugly with all other wires entering from rear. I spent weeks deliberating solution.
Old spark suggested terminating behind CU with floating gland and bringing flying earth lead into CU.
I didn't like the idea to begin with, but could not see anything technically wrong.
At the Intake cupboard it is clearly visible, the EIC details it's SWA.
Maybe you have a similar scenario?
 
You got a link to these 'floating glands'or was it something you fabricated? (Or do you literally mean a gland that is just floating behind)
 
push comes to shove, could gland into a wiska box or galv. conduit box, then link up to CU with appropriate cable, ensuring that the armour is earthed, of course.
 
I wouldn't have done it in the first place.

Why not?

I thought about it for ages but could not think of a better way to get SWA through back of a surface mount CU. I'm always interested to hear alternative ideas as I'm sure I'll get this scenario again. The only way I've found to get around this was flush mount CU with gland, but if this is not possible I really don't know a better way ?
 
Last edited:
I suspect the manufactures instructions for the gland is not to leave it floating adrift from any enclosure, I would C3 that on an EICR.
 
I checked both Niglon and SWA Online and can't find manufacturers instructions. I chose these as this is what is in my tool box. Also no instructions come with these. The only thing on bag is size chart.
I then done a google search and found these guys, their instructions don't mention an enclosure, it just shows how to terminate SWA into their gland.
http://www.cmp-products.com/Installation Instructions/CMP BW.pdf
So I don't see any issue?
 

Reply to EICR Coding - Armour not glanded in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
308
That is what i am going to do. Thanks mate!
Replies
11
Views
689

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top