Hi all been a while but need advice, done an eicr today found that the cooker switch has been left under the plinth so cable not secure etc, tested at the oven which was fine earth wise, what code would this be regarding access and cable security etc, thanks in advance
 
The question is whether the cable is likely to be exposed to possible damage? is anything likely to pull on it? in ideal world everything is clipped but think how many cables run in ceilings and floors without clips...
if the T&E is running under the cupboard behind the kickplate i do not see too much of an issue as long as its securely fastened as it enters the switch, also the switch should be readily accessible, that doesn't mean it has to be on display next to the cooker but if i recall its meant to be within 2metres... at worse i would give a C3 but nothing more.
 
Thanks all for the replys i will inform the landlord tomorrow, and keep you all posted, i understand that an eicr is for safety foremost but sometimes we get situations like this which the regs might not cover specifically
 
With the modern trend of minimal items on display such as switch fuse spurs cooker switches I know a lot of this goes on. At least I would say the switch should be mounted on the side wall of the cupboard and not the flimsy backing so it is readily accessible cough cough. Who would want to start pulling plinths off to gain access to a switch to isolate a cooker or hob when the chip pan is going up in flames?
 

Reply to Eicr cooker switch under cupboards in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
270
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
763
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
765

Similar threads

Although it might appear that I am being elusive with the facts, the point is, only you know what your worth is per hour and how long it will...
    • Optimistic
Replies
3
Views
298
  • Question
When you say plus kettle, does this indicate you are needing 13A socket/s on the island and a hob supply? and then an oven supply on a tall...
Replies
5
Views
685

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top