I was doing a bathroom refurb recently, where the lighting circuit had no cpc. The previous 'electrician', overcome the problem by providing an earth by bonding to a copper pipe in the loft space. However, this 'fix' was spoilt, when the copper pipe was replaced by plastic pipe during the refurb :)
 
Ah yes there is the solution fit another unendorsed sticker notifying the uninitiated, assuming they can speak/read English, job done.

I hope you're not attempting to be facetious Mr. Westy o_O
 
Ah yes there is the solution fit another unendorsed sticker notifying the uninitiated, assuming they can speak/read English, job done.
Yes it is amazing they can imagine a potentially serious safety deficit can be resolved by a sticker with some little English words written on it.
 
how many tenants read the sticker on consumers, not many neither.me speak no ingilsh
do landlords tell the tenants. a yellow sticker wont stop them putting up a class 1
light fitting up with no cpc.
 
how many tenants read the sticker on consumers, not many neither.me speak no ingilsh
do landlords tell the tenants. a yellow sticker wont stop them putting up a class 1
light fitting up with no cpc.
But it's not there property. They should not be making any alterations.?
 
The point of the sticker is for the electrician that next works on the property as the tenants shouldn't be tampering in rhetoric first place.
 
Oops Dave beat me to it, sorry dave I didn't see your post before I started typing.
 
how many tenants read the sticker on consumers, not many neither.me speak no ingilsh
do landlords tell the tenants. a yellow sticker wont stop them putting up a class 1
light fitting up with no cpc.

Even if they had a cpc, those tenants wouldn't know what it was for anyway!
 

Reply to EICR for a rented property with cpc on the lights. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

My latest trick for this....if completely desperate and you have 3 very short cables .... Make a hole big enough for a quickwire to fit through...
Replies
8
Views
793
Definitely, although most likely within the accessories. I've often found that once accessories are disconnected the cabling IR is fine. Sometimes...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top