Couple of years ago did an EICR on a thatched property, satisfactory conclusion with 6 Code 3 observations, some associated with no RCD protection of concealed cables and bathroom lighting circuit etc. (16th Ed).

Now the insurance company wants me to confirm in writing that these issues have been addressed.

Anyone had this problem before? I would like to 'educate' the insurance company to say these would be fixed next time any work is done and being Code 3 not detrimental to safety etc., and in effect with the rate of current changes to regs everybody will have to change their CU every 10 years or so!

Asked Certsure if they could help me with some arguments to go back to the insurance company - wasting my time with them!

Anyone got any 'nuggets'?
 
You carried out the EICR
You made coded observations as per Bs7671
You were only engaged to carry out the EICR (We assume)
And as such were not asked to do remedials.

Without returning to the property (for which you would want payment) and carrying out another EICR, you cannot say at this time whether the remedials that you observed have been completed.
 
Have learnt that many insurance companies will want anything given a coding fixed, but then thats up to the client to decide on, and if they get us to do the work we re-issue the cert with the observations removed.

You should not re issue the cert with the items removed! You should issue an EIC for the work you have done.
For example - To remove all observations from EICR 123456.
As you have carried out installation work to do this.
 
That letter from the insurance company should have been addressed to the homeowner, not to yourself. Your work, in conducting the EICR has been completed and the report issued. As i stated in another thread just today, some insurance companies are hot on thatched roof properties!!


The onus is now on the homeowner to confirm or otherwise whether the said code 3 deficiencies have been addressed or not!! I'm just wondering if the homeowner has informed the insurance company that they have been addressed and stating you were the electrician that addressed them??


I'm not saying that code 3 deficiencies need to be sorted out, that's another matter altogether!!
 
Just to clear up some mis-interpretations. All correspondence from the insurance company has been to the owner. What started all this was that the insurance company told the owner he needed an EICR on his house and annex, and as I did it a couple of years ago he replied to them saying it was done (giving them a copy with the observations listed), however at the time of the EICR it was agreed that the annex wouldn't be tested. So now the insurance compnay wants an EICR on the annex and the Code 3s on the house addressed.

If I advised the customer at the time that the Code 3s needed addressing then he would have said go on and do them! But in my mind they didn't need immediate action.

The only thing I'd have difficulty in arguing with the insurance company is that I ticked the 'needs further investigation' column for a r2 measurement that was a little higher than expected in relation to the r1 measurement - but all Zs measurements on the ring were well within limits. Hence my 'relaxed' attitude to the 'problem'.

Ok I can go back and do that, but one of the Code 3s was for no RCD protection of concealed cables and circuits in a bathroom - 16th edition installation.

As I mentioned before if we go on like this home owmers will need to change their CU every few years to get rid of Code 3s, and the poor customer will need deep pockets, were will it all end?
So there will be some customers thinking we're trying to rip them off with all the new work needed whenever an EICR is done.

For instance with the new Ammendment coming out in January if the 'fire proof CU reg is included' I could Code 3 a plastic CU.
 
Just to clear up some mis-interpretations. All correspondence from the insurance company has been to the owner. What started all this was that the insurance company told the owner he needed an EICR on his house and annex, and as I did it a couple of years ago he replied to them saying it was done (giving them a copy with the observations listed), however at the time of the EICR it was agreed that the annex wouldn't be tested. So now the insurance compnay wants an EICR on the annex and the Code 3s on the house addressed.

If I advised the customer at the time that the Code 3s needed addressing then he would have said go on and do them! But in my mind they didn't need immediate action.

The only thing I'd have difficulty in arguing with the insurance company is that I ticked the 'needs further investigation' column for a r2 measurement that was a little higher than expected in relation to the r1 measurement - but all Zs measurements on the ring were well within limits. Hence my 'relaxed' attitude to the 'problem'.

Ok I can go back and do that, but one of the Code 3s was for no RCD protection of concealed cables and circuits in a bathroom - 16th edition installation.

As I mentioned before if we go on like this home owmers will need to change their CU every few years to get rid of Code 3s, and the poor customer will need deep pockets, were will it all end?
So there will be some customers thinking we're trying to rip them off with all the new work needed whenever an EICR is done.

For instance with the new Ammendment coming out in January if the 'fire proof CU reg is included' I could Code 3 a plastic CU.

What does my head in with some insurance providers is THEM stating the electrical requirements. You've completed an EICR, the summation of which is an overall assessment of the installation, i.e. Satisfactory or Unsatisfactory. To me, that says it all. Recommendations can improve the state of the installation but it has been passed by a suitably qualified person as satisfactory.
 
What does my head in with some insurance providers is THEM stating the electrical requirements. You've completed an EICR, the summation of which is an overall assessment of the installation, i.e. Satisfactory or Unsatisfactory. To me, that says it all. Recommendations can improve the state of the installation but it has been passed by a suitably qualified person as satisfactory.

Insurance companies have the right to ask for all deficiencies to be addressed as they are taking the risk with insuring this thatched roof house, ....or any other property come to that!! They also have the right to cancel the cover on a property, if their conditions are not met!!
 
Just to tie up loose ends.

I suggested the owner 'push back' on the insurance company and they have relented to 2 observations that I did tick 'needs further investigation' box, which seems fair enough!

1) One circuit unable to identify what was being fed

2) The high r2 I mentioned previously
 
Just to tie up loose ends.

I suggested the owner 'push back' on the insurance company and they have relented to 2 observations that I did tick 'needs further investigation' box, which seems fair enough!

1) One circuit unable to identify what was being fed

2) The high r2 I mentioned previously

Seems they bend a bit, then. Further investigation, I can understand. It does leave it in 'no man's land' to a great degree.
 
Always found insurance companies get the wrong end of the stick but then again PIR's / EICR's are not the most clear documents to read for the inexperienced but usually a chat with them sorts the problem or misinterpretation out
 

Reply to EICR & Insurance Companies in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
350
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I don't think I'd use it mate even the one line heading then one long paragraph screams ai. And untrustworthy. I don't think much has been edited...
    • Optimistic
Replies
3
Views
943
NICEIC Certification Scheme Getting accredited to
I am in almost the same boat, although I am registered for a scheme, and as I have been continuously, I have been told no NVQ required... BUT...
Replies
16
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top