Eicr no CPC on lighting circuit | on ElectriciansForums

Discuss Eicr no CPC on lighting circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Joined
Apr 14, 2019
Messages
28
Reaction score
1
Location
Birmingham
Hello, I have been asked to do a eicr on a property that I have found to have no CPC in the lighting circuit. Just wanted to know if this constitutes a c2, or vat best c3. Thank you in advance
 
If only Class 2 items fitted I would C3, if class 1 present then C2.

Even on a C3 I would expand in the comments stating there is a risk and that only class 2 accessories should be fitted and a warning notice displayed on the DB.
 
If only Class 2 items fitted I would C3, if class 1 present then C2.

Even on a C3 I would expand in the comments stating there is a risk and that only class 2 accessories should be fitted and a warning notice displayed on the DB.
Good and great idea Mate but how many Joe Public will take mote of that note on the DB? i suspect none.
 
My GF rents a house, had EICR done they c3 one of the downstairs light fitting metal all earthed and checked continuity all ok, the reason for c3 was no rcd on that circuit because class 1 fitting no other reason.
 
My GF rents a house, had EICR done they c3 one of the downstairs light fitting metal all earthed and checked continuity all ok, the reason for c3 was no rcd on that circuit because class 1 fitting no other reason.
Also the latest edition requires all lighting circuits in domestic to be RCD protected which would attract a C3.
 
Circuits supplying luminaries in domestic installations require additional protection by an rcd, it’s irrelevant if the fitting is a pendant or not.
It’s a C3 regardless of class of luminaries.
 
Just goes to show the inconsistency of these reports, bit like the government.
Remember the rcd is for additional protection, the fact that is plastic or metal has no bearing, it is a requirement for domestic installations so should always be highlighted as a code, now if it’s metal and has no fault protection to it for ADS then it’s a C2, this would be a C2 even if an rcd was present.
 
Remember the rcd is for additional protection, the fact that is plastic or metal has no bearing, it is a requirement for domestic installations so should always be highlighted as a code, now if it’s metal and has no fault protection to it for ADS then it’s a C2, this would be a C2 even if an rcd was present.
Im not disagreeing with you, just stating what the electrician said if all the fittings were class 2 he would not have coded at all.
 
OP sorry to have hijacked your post, but think along the situation I have described, then make your own mind up on how to code your situation.
 
I did one only 2 months ago. It had RCD protection but no cpc to lights or switches through out C3. Regardless of whether or not joe public take heed of what labels are on C/U if you have fulfilled your duty and warned them that only plastic class 2 switches and fittings can be used you have covered yourself. I also fitted plastic covers over screws on the switches so there was no metallic parts accessible to touch. I also took a picture of the C/U afterwards with the labels attached clearly showing no cpc warning label and circuits it related to.
 

Reply to Eicr no CPC on lighting circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
917
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

My latest trick for this....if completely desperate and you have 3 very short cables .... Make a hole big enough for a quickwire to fit through...
Replies
8
Views
790
It’s difficult to advise on an electrical issue when some isn’t very conversant with electrical terminology.
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top