Hello, I have been asked to do a eicr on a property that I have found to have no CPC in the lighting circuit. Just wanted to know if this constitutes a c2, or vat best c3. Thank you in advance
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Eicr no CPC on lighting circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Good and great idea Mate but how many Joe Public will take mote of that note on the DB? i suspect none.If only Class 2 items fitted I would C3, if class 1 present then C2.
Even on a C3 I would expand in the comments stating there is a risk and that only class 2 accessories should be fitted and a warning notice displayed on the DB.
There is a published testing and inspecting procedure for your situation
The outcome will determine what you decide. Thank for the reply. Where can I find this
Also the latest edition requires all lighting circuits in domestic to be RCD protected which would attract a C3.My GF rents a house, had EICR done they c3 one of the downstairs light fitting metal all earthed and checked continuity all ok, the reason for c3 was no rcd on that circuit because class 1 fitting no other reason.
The guys said to me if it was class 2 eg pendant no code.Also the latest edition requires all lighting circuits in domestic to be RCD protected which would attract a C3.
Just goes to show the inconsistency of these reports, bit like the government.Circuits supplying luminaries in domestic installations require additional protection by an rcd, it’s irrelevant if the fitting is a pendant or not.
Remember the rcd is for additional protection, the fact that is plastic or metal has no bearing, it is a requirement for domestic installations so should always be highlighted as a code, now if it’s metal and has no fault protection to it for ADS then it’s a C2, this would be a C2 even if an rcd was present.Just goes to show the inconsistency of these reports, bit like the government.
Im not disagreeing with you, just stating what the electrician said if all the fittings were class 2 he would not have coded at all.Remember the rcd is for additional protection, the fact that is plastic or metal has no bearing, it is a requirement for domestic installations so should always be highlighted as a code, now if it’s metal and has no fault protection to it for ADS then it’s a C2, this would be a C2 even if an rcd was present.
I was disagreeing with the electrician ha.Im not disagreeing with you, just stating what the electrician said if all the fittings were class 2 he would not have coded at all.