not sure yet im going to the job Monday all I know is its a dental surgery, with no rcd protection an any circuit gas is bonded and so is water,,need to check special locations yet as to if its classed as a medical location,, but because its not to current regs either ensure cross bonding is done and use eebads or upgrade to rcbos and its covered but just thinking of cost as thers about 8-9 db's
 
well I thought your methods of fault protection were eebads if thers no rcd protection,, and ads no rcd protection if its fully contained exept for socket outlet or if its monitored by a competent person
 
are you Zs readings compliant with BS7671 disconnection times for each circuit? if so you just give the lack of RCD protection a code C3, unless the use of any sockets ( e.g. outdoors ) warrants a code C2, or if there's no supp. bonding in special locations ( also a C2).
 
its my dads business, I want to do wats right and least costly but it im, see all I usually do is report back recommendations to the office, and they take it from ther but this is a good opportunity for me to delv alittle deaper into the regs and learn something aswell,,eeb earth equipitential bonding,,, lol yes is got it wen u said I I automaticly assumed cross bonding, which because I trained to the 17th and im mainly on new install don't really come across it
 
Hehe, got you :)
I note you're concerned about cost but have you seen how much those buggers charge?
Probably not because your dad fixes your teeth
 

Reply to eicr on premsis with no rcd in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
759
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
748

Similar threads

Duh!!! Just re-read Op's original post, it was converted to a RFC!
Replies
12
Views
681
Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top