Improvement recommended, due to regulatory changes. No work needs to be carried out and nothing is potentially dangerous.
...
Absolutely - in just the same way when we find an installation that has the old black and red colours - due to regulatory changes we also must highlight this as a C3 - Improvement Recommended.
After all if the regulations do change making previously acceptable aspects no longer compliant, then it has to be across the board, if we must highlight one particular thing as C3 because it's non-complient we must apply this globally applying C3s on everything that is no longer completely compliant with the latest version of the regs.
Of course the customer doesn't have to address the 10-20 C3s or whatever results from the automatic C3 for anything not completely in line with the most recent regs.
OR
Should we apply engineering judgements based on the current version of the regs?
So red & black wiring, although not in line with current regs, wouldn't actually be an issue whatsoever, - changing to the new colours wouldn't really improve anything from a safety, usability, or end user point of view - so why Recommend an improvement when there actually isn't any real improvement.
Similarly, if the RCD type isn't an issue in this application again if changing it wouldn't really improve anything from a safety, usability, or end user point of view - why Recommend an improvement when there actually isn't any real improvement.
On the other hand if the RCD is on circuits that would benefit from changing the type this would be an improvement, anything from a safety, usability, or end user point of view, so deserves a C3.
On the other, other hand (?) If the RCD is actually being blocked by dc, (or clearly almost certainly will be blocked - say on a circuit where the customer uses a silly "granny charger") - then it becomes a C2
This is my problem btw with many questions about "I have x, what code?" - the answer is C1, C2, C3 or nothing for the same "issue" even on the same site depending upon the circumstances.
An easy example is "premature wiring collapse" - a drooping cable across an entrance is C1, a cable affixed, but which would drop across an exit in the event of a fire, would be C2, a cable affixed, but which would drop along a wall - out of the way in the event of a fire, would be C3, or a cable affixed, but which would drop down just a few inches - well out of harms way in the event of a fire, wouldn't attract anything.