EICR question, OLD AC RCD- code 3 or no code? | Page 3 | on ElectriciansForums

Discuss EICR question, OLD AC RCD- code 3 or no code? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

@Julie.

My thinking, the capacity of which is limited, is that potential for issue exists due to the way in which this protective device operates and the fact that one new appliance has the potential to change that operation.

I take the above points, but believe old wiring colours aren't a good comparison as they will have no impact on a householder who doesn't tinker with fixed wiring in their home. Replacement of an old or failed appliance doesn't generally require consultation. Given that a significant number of domestic EICRs are carried out for the sole reason of complying with rental legislation, I feel this adds another layer to the issue as no one can look around the property and assume risk on the basis of appliances present at time of inspection.

Similarly, the issue of premature collapse doesn't generally involve variables - risk exists or it does not and remedial work is quite simple.

Furthermore, most inspectors who carry out EICRs won't have any means of detecting DC leakage, much less any interest in attempting to do so.

What I have taken away from this discussion is that a number of opinions in favour of not coding type AC RCDs are based on customer reaction. While I understand that position, I don't consider customer sensibilities to be a factor of testing and inspecting. It's an interesting discussion about what, on the surface, appears to be a simple issue.
 
Another way to look at this might be that if we do not code an item as C3 because it complied at the time of installation, we are taking away the client's choice to make a significant improvement to the safety of the installation. They would be unaware of the improvements made to the wiring regulations, and of changes that are happening in the world of technology that can both contribute to safety, but also to introduce new potential hazards (in this case the DC blinding of older RCDs).
Coding it C3 at least makes the client aware that an improvement to the safety of the installation is actually an option.
That's an interesting way of saying 'covering my arse' :)
 
But that would be at the inspector's discretion?

Now that you raise this point, I can't help wondering if it is possible to issue a satisfactory report containing a C2?
I think the point is C2 is an immediate "unsatisfactory" due to a clearly identified danger following a single fault, whereas C3 are not that dangerous in themselves.

But if you found an installation where practically everything was so rubbish it merited C3 you might come to the conclusion that overall it is not to a satisfactory degree of safety.
 
I think the point is C2 is an immediate "unsatisfactory" due to a clearly identified danger following a single fault, whereas C3 are not that dangerous in themselves.

But if you found an installation where practically everything was so rubbish it merited C3 you might come to the conclusion that overall it is not to a satisfactory degree of safety.

I read more on this last night and it makes perfect sense when viewed in black and white.
 
My interpretation is that anything that is not to the current version of the regs merits at least a C3. Every reg change should hopefully be an improvement, so anything which hasn't incorporated that improvement should be coded 'improvement recommended'.
There are many things I've installed in complete compliance with the regs that a few months later would attract a C3 on an EICR.
The plastic cased CUs in all my properties except one is an example that comes to mind, and now the type AC RCDs in those CUs.
 
I then said - in that instance how would you code a voltage operated ELCB- it complied with the regs at the time of the install and you can test it with an RCD tester and the test button works so....
Going back to this point...
In almost all cases I consider this a legitimate C2, as:
...the chances are there'll be a lower impedance fault path via any metal services than via the earth rod, and the VOELCB needs current to flow via the earth rod to operate
...it will do nothing at all about a human caught between live and real earth

So we are only one step away from live parts and no ADS unless the Ra is exceptionally good.
As they were removed for safety reasons about 37 years ago I doubt I'd get as far as coding it - I'd just replace it.

Have you ever got one to trip with an RCD tester btw? I'd assume it would need more than 30ma to do anything as it's basically a solenoid.
 
Last edited:
It's been decades since I came across a VOELCB, but I changed them on sight back then, so it's definitely a C2 if I found one now. They are not residual current devices, so I believe C2 is entirely justified.
Might be entirely wrong, but I have a recollection that the voltage operated devices had a resistance of around 60 ohms, so about 1.8V on the earth wire to trip it off.
 
Might be entirely wrong, but I have a recollection that the voltage operated devices had a resistance of around 60 ohms, so about 1.8V on the earth wire to trip it off.
Completely academic now, I know....one of my very old books says the requirement was based on the Ze, if 200 ohms then tripping at <=24v was required and if 500 ohms it had to trip at <=40v.
The 14th Edition says the correct test is a test voltage not exceeding 45v applied to N and E on the installation side and it must trip instantaneously.
It may be that manufacturers did a lot better than the minimum requirement though!
 
C3 for me & in all case’s regarding now & then situations…it covers your opinion/competence & is a recommendation for improvement in so many “grey” areas the Regs present to us those situations
 
BS7671 is not retrospective (from memory page 4 states that) , however we do code the the current edition of the regs as stated in GN3.
to answer the question you have to assess the risk ,if only pure resistive loads are on an AC rcd no code or maybe fyi only, i would code C3 if other loads are present that don’t affect the testing of the (RCD) Residual Current Device at time of test,C2 if it causes rcd blinding and it does not function correctly.
 
I hate the description of the Regulations "not being retrospective". No such comment is made within the Note from the HSE. What it actually states is that compliance with previous iterations of the Regulations may not necessarily imply that the installation is now unsafe or that it requires upgrading. As such, it also doesn't rule out that aspects of it might actually be unsafe or require upgrading.
 
Looking at a MEM A100HE RCD earlier today (of which I've fitted many dozens over the years), and was surprised to see it caries the type A (sine wave over half sine wave) markings.
How long have type A RCDs been around? I assumed it was a relatively new thing.
This was a newer grey one, but I've looked at an older yellow one, and still the same markings.
 

Reply to EICR question, OLD AC RCD- code 3 or no code? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
714
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

Hello all easy cert users, ive been using easy cert since 2001 with no yearly subscription. and also found other people looking for older versions...
Replies
0
Views
115
  • Question
If they got a shock then something cannot have been isolated.
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top