Just wondering if this is acceptable?? tails for an extra cu taken straight off incoming armoured cable.

[ElectriciansForums.net] EICR question...see pic
 
If its an swa feed the obvious question would be are the tails ccc suitably rated and does the other cu still meet max zs requirements of the OCPD. One time i would C2 this if its done on the main switch off a consumer unit tailed directly into meter therefore loosing your single point of isolation to the installation. I see no issue with the cables pushed into the double screwed terminal aslong no cores have been loped off to get them in.
 
To me if it’s a C1 code then the rules of basic insulation has failed and it is an immediate danger and risk of electric shock.
A C2 code if a another fault either Electrical or non Electrical could introduce a dangerous situation and fault protection or basic protection may not be achieved.
C3 if it is a non compliance and introducing remedial works will render it safer for the user and the general environment it operates in.

So for people to say it’s a C2 I don’t understand.
 

Reply to EICR question...see pic in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
400
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
986
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

yes it was a pee-take... I was commenting if someone was dumb enough to use earth clamps on armour, they might just be dumb enough to earth a...
Replies
6
Views
513
  • Question
Thank you, that's a really helpful post, nice & clearly stated and helps me clear up a lot of confusion on this matter.
2 3 4 5
Replies
65
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top