EICR question | on ElectriciansForums

Discuss EICR question in the UK Electrical Forum area at ElectriciansForums.net

Joined
Sep 5, 2014
Messages
99
Reaction score
17
Location
Wilts
Hi chaps,

This may have been asked before but i cant seem to find it when searching so im sorry if someone easily finds it.

Im currently carrying out a EICR at a commercial premises and the water is bonded from a sub DB and not the MET, its something that i understand needs to be noted but is it something that needs to be coded? If so what code?

Thanks
 
I think reg 542.4.1 applies : "in every installation a met shall be provided to connect the following to the earthing conductor - CPCs - protective bonding conductors ... etc"

My 20p worth : the existing arrangement is not in accord with 542.4.1 and so I would give it a C3, as it is not unsafe (for you to confirm with testing?) but it would be an improvement to comply with regulations.

I'm not expert in this one, and others please feel free to jump in :)
 
I say that as long as the water pipe (if extraneous) is connected to the MET by conductors that comply along the whole route with the requirements of protective bonding conductors, it doesn't matter if they go via one or more other terminals.

542.4.1 doesn't say that all CPCs, protective bonding conductors, etc. have to be connected directly to the MET. In fact most CPCs won't be connected directly to the MET.
 
Hi chaps,

This may have been asked before but i cant seem to find it when searching so im sorry if someone easily finds it.

Im currently carrying out a EICR at a commercial premises and the water is bonded from a sub DB and not the MET, its something that i understand needs to be noted but is it something that needs to be coded? If so what code?

Thanks
Hi akwoody2 have the Mods got your profile correct because you are down as DIY, I have to ask because if you are actually a DIY Member do you think you should be doing EICRs?
 
Hi akwoody2 have the Mods got your profile correct because you are down as DIY, I have to ask because if you are actually a DIY Member do you think you should be doing EICRs?

Hi Pete,

I'm a fully qualified electrician, not to sure why I'm down as DIY. Maybe something to do with me not putting my qualifications in yet?

Do you have an opinion on the bonding to the water?
 
Hi Pete,

I'm a fully qualified electrician, not to sure why I'm down as DIY. Maybe something to do with me not putting my qualifications in yet?

Do you have an opinion on the bonding to the water?
Well it is connected to the MET in a round about way, without seeing the job it's quite hard to form an opinion, as for your profile, best you get it updated, the wrong,or no info can lead to incorrect or sometime abusive answers, the non filling out of profile info is a pet hate of mine, I have posted before requesting correct profile info is a must, but quite rightly you can't make people provide info if they don't want to.
 
Well it is connected to the MET in a round about way, without seeing the job it's quite hard to form an opinion, as for your profile, best you get it updated, the wrong,or no info can lead to incorrect or sometime abusive answers, the non filling out of profile info is a pet hate of mine, I have posted before requesting correct profile info is a must, but quite rightly you can't make people provide info if they don't want to.


I'll get it done for you tonight Pete!
 
So is the amour acting as a cpc and bonding conductor

Well if you read the post its obvious it is being used as that at the minute! But incorrectly so, 16mm 4c has steel equivalent of 72mm which in terms of copper equivalent is inaquate in terms of being <10mm. I would back you up in a C2 observation on that observation.
 
Well if you read the post its obvious it is being used as that at the minute! But incorrectly so, 16mm 4c has steel equivalent of 72mm which in terms of copper equivalent is inaquate in terms of being <10mm. I would back you up in a C2 observation on that observation.

Thanks. Out of interest how did you get to it being the equivalent of <10mm?
 

Reply to EICR question in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
277
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
269
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
350

Similar threads

Understood, ; ) i'll pass it on to a company who do them day in day out i think.
Replies
8
Views
820
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
928

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top