Hi chaps,

This may have been asked before but i cant seem to find it when searching so im sorry if someone easily finds it.

Im currently carrying out a EICR at a commercial premises and the water is bonded from a sub DB and not the MET, its something that i understand needs to be noted but is it something that needs to be coded? If so what code?

Thanks
 
Find the csa of the armouring on data charts provided by manufacturers then divide by 8.8 to convert to equivalent copper csa conductor. Out of intrest how would you go about correcting this? Are you going to reroute/extend bond back to MET or add an additional cable to the EMT to and leave bond in place?
 
Find the csa of the armouring on data charts provided by manufacturers then divide by 8.8 to convert to equivalent copper csa conductor. Out of intrest how would you go about correcting this? Are you going to reroute/extend bond back to MET or add an additional cable to the EMT to and leave bond in place?

I'd run it back to the MET as it's not actually that far away
 
Last edited:
Find the csa of the armouring on data charts provided by manufacturers then divide by 8.8 to convert to equivalent copper csa conductor. Out of intrest how would you go about correcting this? Are you going to reroute/extend bond back to MET or add an additional cable to the EMT to and leave bond in place?

So by calculation you would need a 70mm 4 core to get the equivalent of 16mmcpc. How come we see so many sub mains being ran with the steel being the cpc if it doesn't comply?
 
So by calculation you would need a 70mm 4 core to get the equivalent of 16mmcpc. How come we see so many sub mains being ran with the steel being the cpc if it doesn't comply?
Because people don't understand that just because the armour has a large csa it isn't necessarily adequate to support bonding. Rule of thumb times your bonding size by 8 to get the required size of armour, GN8 has all the info. If you have a four core cable less than 50.0 it will be inadequate to support the minimum size of 10.0 bonding
 
Find the csa of the armouring on data charts provided by manufacturers then divide by 8.8 to convert to equivalent copper csa conductor. Out of intrest how would you go about correcting this? Are you going to reroute/extend bond back to MET or add an additional cable to the EMT to and leave bond in place?

The cpc also needs upgrading for the 100a supply to the sub board
 
Putting on my student's tin hat, I'll give it a bash :

For bonding we are concerned about touch voltages and so the path must be comparable to the resistance of Cu and so we use resistivity ratios (>8). For use as CPC we use the adiabatic eqn and its k factors that include temp rise and thermal capacity of the materials. This gives a reduced steel requirement compared with bonding calcs and so SWA armour is often ok for CPC but not for bonding.
 
So by calculation you would need a 70mm 4 core to get the equivalent of 16mmcpc. How come we see so many sub mains being ran with the steel being the cpc if it doesn't comply?

Because CPC size is calculated by the adiabatic equation and not by the equivalent conductivity method used for bonding. the CPC only has t carry fault current for a specified time which is limited by the fault protection device and so can be a lot smaller than the bonding conductor required on TNCS.
 
Sorry, a combination of me not following the thread correctly, reading it in my phone with a cracked screen and getting completely mixed up. Cpc is correct and won't need to be altered. As for the bonding it's not man enough so a recommendation will need to be put down
 
Pete that's a link to the pdf copy in a folder on your PC desktop. So hopefully inaccessible to the outside world.
And I suspect admins will not allow a copy on the forum of any of its content due to copyright.
 
Pete that's a link to the pdf copy in a folder on your PC desktop. So hopefully inaccessible to the outside world.
And I suspect admins will not allow a copy on the forum of any of its content due to copyright.
Oh sorry I thought I had posted a copy of the chart, can admin please delete
There is a comparison chart in the OSG
file:///C:/Users/Pete/Desktop/Electrical%202/SWA%20CPC.pdf
Admin can you please delete my reply
 

Reply to EICR question in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
281
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
270
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
351

Similar threads

Understood, ; ) i'll pass it on to a company who do them day in day out i think.
Replies
8
Views
820
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
928

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top