If a shower was fitted 15 years back and had no rcd what cat would it be on a eicr
 
i can see why he has done that!! as MOST showers stipulate protection by RCD...

end of the day the PIR is based on what you deem safe/unsafe.... nobodys decisions or suggestions should influence YOUR decision
 
Well if there is no supp bonding and that was required to limit the different potentials of exposed metalwork then this is potentially dangerous so I would code it as a C2 unless there was an RCD fitted to all circuits in the bathroom and main bonding was present.
What you have to watch for here IMO is that while the electrical installation (fuseboard etc) maybe as they were when installed, most often the bathroom has had a make over -during which the supp bonding was not re-installed. In this case the person ordering the work has a choice re-instigate the supp bonding or upgrade board (and bonding).

From 4. Periodic inspection of existing domestic and similar installations : Electrical Safety CouncilQ4.4
What Classification Code should be given if it is found that there is no supplementary bonding in a bathroom having extraneous- or exposed-conductive-parts, and the conditions given in Regulation 701.415.2 for its omission are not met?
[FONT=&amp]Classification Code C2. Where the presence of supplementary bonding cannot be confirmed by inspection, it may be verified by a continuity test (< 0.05 ?)[/FONT]
 
Not according to the ESC Electrical Safety Council
From 4. Periodic inspection of existing domestic and similar installations : Electrical Safety CouncilQ4.4
What Classification Code should be given if it is found that there is no supplementary bonding in a bathroom having extraneous- or exposed-conductive-parts, and the conditions given in Regulation 701.415.2 for its omission are not met?
[FONT=&amp]Classification Code C2. Where the presence of supplementary bonding cannot be confirmed by inspection, it may be verified by a continuity test (< 0.05 ?)[/FONT]
 
Not according to the ESC Electrical Safety Council
From 4. Periodic inspection of existing domestic and similar installations : Electrical Safety CouncilQ4.4
What Classification Code should be given if it is found that there is no supplementary bonding in a bathroom having extraneous- or exposed-conductive-parts, and the conditions given in Regulation 701.415.2 for its omission are not met?
Classification Code C2. Where the presence of supplementary bonding cannot be confirmed by inspection, it may be verified by a continuity test (< 0.05 ?)

The OP didn't mention supplementary bonding!!
 
But he is talking about Regulation 701.415.2 and this is conditional on whether the install meets the regs in force at the time - so it is pertinent that the Supp boning should be met - if it is then it is a C3 possibly if not it is certainly a C2 according to the advice from the esc
 

Reply to Eicr question in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
372
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
937
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I usually put something like this To assess compliance with BS7671 for continued safe operation (5 year periodical inspection)
Replies
8
Views
450
  • Question
No it is not implying it is safe, it is stating what the recommended date for the next inspection is. The next inspection date sticker doesn't...
Replies
10
Views
2K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top