Discuss EICR RCD 63A exceeded by breaker total code in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
But was this applicable in 2012?An upfront ocpd of the rcd should be equal to or less than the current rating of the rcd, if the combined mcb’s downstream of the rcd have the potential to exceed the ccc of the rcd, then it should be coded on an EICR .
Diversity of the final circuits alone is no longer acceptable for providing overload protection of an rcd.
This is also applicable to main switch disconnectors to BSEN 60947-3
It does not matter, what matters is the question "is there a real risk?"But was this applicable in 2012?
That’s the point, a 63 amp rcd won’t trip if it gets 100amps pulled through it, you could wack 1000 amps through it and it will just melt rather than trip.If a 63a rated RCD gets a C3, then a lot , if not most, new populated boards supplied now would warrant a C3 the minute they are fitted.
I would say that if a board comes with 2 x 632 RCDs then that is as manufactured and attracts no code whatsoever. The 63a refers to the current that it can interrupt without being damaged, if it trips with say 100a flowing through it, it will more than likely get damaged and have to be replaced. But it would have done its job.
Thermal damage to any components in a CU, not just RCDs would require at least C2, so that’s not really relevant.
You may well be right Ian, but my point is that if you purchase and fit a new populated board such as below, you would need to put down the RCDs as a departure from the reg's. I would say that they were manufactured to a BS and fitted as per manufacturer's instructions.That’s the point, a 63 amp rcd won’t trip if it gets 100amps pulled through it, you could wack 1000 amps through it and it will just melt rather than trip.
I suspect the reason this regulation changed is all the burnt out 63 amp rcd’s having 8plus circuits hanging off them.
It has No overload protection other than the upfront protection device.
A C3 at most without evidence of thermal damage in my opinion.
63A relates to it's continuous running duty in normal operation. It's breaking capacity will be considerably higher into KAs so switching a 100A load is not likely to cause any damage.If a 63a rated RCD gets a C3, then a lot , if not most, new populated boards supplied now would warrant a C3 the minute they are fitted.
I would say that if a board comes with 2 x 632 RCDs then that is as manufactured and attracts no code whatsoever. The 63a refers to the current that it can interrupt without being damaged, if it trips with say 100a flowing through it, it will more than likely get damaged and have to be replaced. But it would have done its job.
Thermal damage to any components in a CU, not just RCDs would require at least C2, so that’s not really relevant.
Not really. You would be able to purchase and install this board if the design of the installation permitted it to be installed in line with the said requirements for overcurrent protection of the RCDs.You may well be right Ian, but my point is that if you purchase and fit a new populated board such as below, you would need to put down the RCDs as a departure from the reg's. I would say that they were manufactured to a BS and fitted as per manufacturer's instructions.
View attachment 64824
View attachment 64825
Thanks for that clarification Westward, I suppose that a board with a 100a main switch and 2 x RCDs is designed for a fairly balanced load over the two RCDs. I don't think I'll be coding this anytime soon unless I think one of the RCDs is likely to have more than 63a running through it by design. I've never come across this, most of the domestic installations I test don't even have 50a as maximum demand.63A relates to it's continuous running duty in normal operation. It's breaking capacity will be considerably higher into KAs so switching a 100A load is not likely to cause any damage.
True Loz but the OP was just adding up the ratings of the MCBs and the boards illustrated both come with MCBs totalling near or over 200a. So it would be impossible to satisfy the regs as being described here.Not really. You would be able to purchase and install this board if the design of the installation permitted it to be installed in line with the said requirements for overcurrent protection of the RCDs.
Otherwise you would have to specify a different board for that particular installation.
Reply to EICR RCD 63A exceeded by breaker total code in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net