Just done an EICR on an outbuilding that is habitable (kitchen/wetroom etc). Supply is taken from henly block in the meter cupboard, via 2 core SWA to building. At building SWA is glanded into a metal box but the box (earth) is not connected to the plastic consumer unit which sits right next to the metal box. Ze for the outbuilding rod is 350ohms.
So I've got 2 problems, 2 earths (house PME) and outbuilding (TT) in close proximity and the TT giving a poor reading.
Water supply to outbuilding is in plastic pipe and in the outbuilding the connected copper pipework is bonded.
Whats stopping me using the SWA to provide the PME earth to the outbuilding, to fix both problems? I know the water pipes are bonded but they are not extraneous, although I haven't done the test to confirm.