Eicr ring main readings | Page 2 | on ElectriciansForums
Discuss Eicr ring main readings in the UK Electrical Forum area at ElectriciansForums.net
cliffed
Worcester
Would you guys be happy with these readings on ring main,Rcbo c type 30ma/32 amp.
r1 1.87...rn 1.91 cpc 3.20....R1 +R2.1.26.
zs 1.46 ohms.
Sorry to hijack the post but for someone still learning how do you work out the length of circuit from the readings ie what would the formula be please ? Tia
Look in the on-site guide, appendix, I think it's table 11
It gives the R1+R2 resistance per metre
So for 2.5/1.5 it's around 19.5 miliohm per metre if you know the length, it's length x this value, if you know the overall resistance it's the resistance devided by the resistance per metre
You could also work it out from R1 for 2.5mm2 per metre, plus R2 for 1.5mm2 per metre
These values are also in the table
For a ring final, use an end-to-end reading, eg. the line conductor r1.
Length of conductor = resistance of conductor Ă· resistance of conductor per meter
For a 2.5mm² conductor, resistance per meter is 7.41mΩ, or 0.00741Ω. So:
Length of conductor = r1 Ă· 0.00741
Reply to Eicr ring main readings in the UK Electrical Forum area at ElectriciansForums.net
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
OLDBOY
O
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...