Hi, recently had an EICR test done by 'Landlord Certificates' which failed due to circuite 3 having two radial circuits into a single 32amp MCB, they advised splitting it into two 20amp MCB's and quoted Ā£174 including EICR certificate. The Electrian appears to have simply taken out the 32amp MCB's and put in a 20amp and 16amp. Was the original actually a fail? And is what the Electrician has done now acceptable?
[ElectriciansForums.net] EICR Test Fail, before and after
 
Downsizing a breaker isn't going to make it unsafe, unless that circuit is needed for critical safety reasons.

Personally, I would have made an effort to repair what looks like 2 RFCs at the least.

They also could have made the effort of splitting the lights and RFCs between the RCDs.
 
Last edited:
Sorry - did not see the latest posts today - much of below has already been commented on...
Perhaps I am missing something but I am puzzled as to why the MCB on circuit 4 has changed.
Looking at the 'before' photograph both MCB3 (32A) and MCB4 (32A) have two red line wires, suggesting (but not confirming) the existence of two ring circuits.
The original post makes no mention of a change to circuit4/MCB4 but this has changed to a 16A MCB in the 'after' photo but seems to indicate that a single 32A MCB is to be replaced by two off, 20A MCBs.
I wonder if one of these circuits (circuit4?) is still a ring which may now be susceptible to tripping as the MCB is only 16A. Obviously depends on the load on the circuit.
 
Downsizing a breaker isn't going to make it unsafe, unless that circuit is needed for critical safety reasons.
Sorry - did not see the latest posts today - much of below has already been commented on...
Perhaps I am missing something but I am puzzled as to why the MCB on circuit 4 has changed.
Looking at the 'before' photograph both MCB3 (32A) and MCB4 (32A) have two red line wires, suggesting (but not confirming) the existence of two ring circuits.
The original post makes no mention of a change to circuit4/MCB4 but this has changed to a 16A MCB in the 'after' photo but seems to indicate that a single 32A MCB is to be replaced by two off, 20A MCBs.
I wonder if one of these circuits (circuit4?) is still a ring which may now be susceptible to tripping as the MCB is only 16A. Obviously depends on the load on the circuit.
Without actually testing to see if itā€™s a ring or some radials feeding an immersion or something itā€™s hard to say but changing it for a 20 I canā€™t see doing any harm

Is there no labelling on the cu ?
 
Just to follow up on this, circuit three was indeed a ring that lost it's continuity, the work quoted for was to split this into two 20amp circuits with separate MCB's, instead they just replaced the MCB for a 20amp MCB, is this OK?

It actually looks like they have also downgraded circuit four to a 16amp MCB, this is presumably a ring that actually does have continuity, the guy who did the work did no testing after so this is obviously speculation, but could this potentially be unsafe?
It is extremely potentially unsafe if downrating the MCB on the incomplete ring is all they did, without ensuring that the faulty section of the ring is completely disconnected at each end.
Whether a single 20A MCB for both sections, and a 16A for the other is satisfactory depends on the calculated or estimated load for those circuits. If it is reasonably expected that the load on those circuits would exceed 20A or 16A respectively for more than a few minutes, then it is not satisfactory.
 
Could also be that the cables for the the 2 rings are in wrong The mcbs
As one leg from one ring in with other ring and same on other MCB
Yes I have come across this a lot after someone has done a board swap and they got the rings mixed up.
Very easy to spot as if you turn one Off one 32amp MCB off both Rings still remain On Live.
 
Yes I have come across this a lot after someone has done a board swap and they got the rings mixed up.
Very easy to spot as if you turn one Off one 32amp MCB off both Rings still remain On Live.
Yup they have not end to end tested or they have and crossed the legs up I always double check and mark the legs for each RFC. So simple for a few minutes work.
 
The best one I had recently was 2 circuits, 1 ring and 1 16 A radial but one leg of the ring was in the 32A along with the shed radial and the other leg of the ring was in the 16A MCB marked shed supply. Not only that the board was a mismatch of MCB's and the only way they could get some to fit was put them in upside down so when they were switched on they were all pointing different ways, oh and the board was mounted sideways.

That was fun trying to get the power to go off, had to switch the main switch off and then sit down and try and work out what on earth was going on.
 
A side ways mounted board with numerous makes of breakers with some mounted upside down and some sharing the same circuit.

That is some kind of special
 
So sorry to resurrect this again, I still haven't got it resolved so I'm going to give up on the current Electrician and find a new one, he was supposed to come fix it but never turned up.

Anyway I bought one of those socket testers off Amazon just to see if there were any obvious faults and discovered something I think is odd.

On the image below I have labelled up the CU -

[ElectriciansForums.net] EICR Test Fail, before and after


This is how it's labelled on the cover-
Circuit 1 - Cooker
Circuit 2 - Central Heating, NOTE: when turned off the boiler stays on
Circuit 3 - One Double socket in Bedroom 2, NOTE: when turned off boiler goes off too
Circuit 4 - Two Double sockets in living room, Two double sockets in Bedroom 1, and One Double Socket in Bedroom 2
Circuit 5 - Two double sockets in same cupboard as CU, and two Double sockets in Kitchen
Circuit 6 - Lights
Circuit 7 - Extractor Fan
Circuit 8 - Two Double sockets in Hallway

So it seems circuit 3 is a ring that serves just one socket, and the boiler. No clue what wire is in the central heating circuit, turning it off doesn't seem to turn anything off.

I'd like to get this tidied up and safe, plus I still need an EICR, when looking for a new electrician what do I tell them? It's not a full rewire is it?

It doesn't need to look like some piece of art but I'd like it to be of a standard where I'm not embarrassed to post a photo of it. Can I assume circuit 3 just needs to be turned into a radial, the boiler put into circuit 2, and a 32amp MCB added back to circuit 4, and then a tidy up?

Thanks so much for all the info posted, the electrician that did this was giving me the run-around, I was able to have a basic discussion about rings and radials and he backed down and admitted a mistake was made.

Cheers
 
Last edited:
So sorry to resurrect this again, I still haven't got it resolved so I'm going to give up on the current Electrician and find a new one, he was supposed to come fix it but never turned up.

Anyway I bought one of those socket testers off Amazon just to see if there were any obvious faults and discovered something I think is odd.

On the image below I have labelled up the CU -

View attachment 108529

This is how it's labelled on the cover-
Circuit 1 - Cooker
Circuit 2 - Central Heating, NOTE: when turned off the boiler stays on
Circuit 3 - One Double socket in Bedroom 2, NOTE: when turned off boiler goes off too
Circuit 4 - Two Double sockets in living room, Two double sockets in Bedroom 1, and One Double Socket in Bedroom 2
Circuit 5 - Two double sockets in same cupboard as CU, and two Double sockets in Kitchen
Circuit 6 - Lights
Circuit 7 - Extractor Fan
Circuit 8 - Two Double sockets in Hallway

So it seems circuit 3 is a ring that serves just one socket, and the boiler. No clue what wire is in the central heating circuit, turning it off doesn't seem to turn anything off.

I'd like to get this tidied up and safe, plus I still need an EICR, when looking for a new electrician what do I tell them? It's not a full rewire is it?

It doesn't need to look like some piece of art but I'd like it to be of a standard where I'm not embarrassed to post a photo of it. Can I assume circuit 3 just needs to be turned into a radial, the boiler put into circuit 2, and a 32amp MCB added back to circuit 4, and then a tidy up?

Thanks so much for all the info posted, the electrician that did this was giving me the run-around, I was able to have a basic discussion about rings and radials and he backed down and admitted a mistake was made.

Cheers

Is circuit 3 a ring ? Or is it already a pair of radials ?
Is the feed to the boiler via a fcu ?
What type of boiler is it ?
Do you have an immersion tank heater ?
 

Reply to EICR Test Fail, before and after in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
454
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

There is one reason to have an inspection every three years instead of the five. Itā€™s more work and money for them šŸ˜šŸ˜
Replies
15
Views
2K
Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top