HappySlappy
DIY
Hi, recently had an EICR test done by 'Landlord Certificates' which failed due to circuite 3 having two radial circuits into a single 32amp MCB, they advised splitting it into two 20amp MCB's and quoted Ā£174 including EICR certificate. The Electrian appears to have simply taken out the 32amp MCB's and put in a 20amp and 16amp. Was the original actually a fail? And is what the Electrician has done now acceptable?