From memory the cable comes through wall from bathroom (or maybe down from ceiling) and runs along inside wall of airing cupboard, fixed to wall by clips, then into power shower pump. So not subject to movement or rubbingUnless the cable is likely to be or is prone to mechanical damage then no. Is the cable actually fixed.
From memory the cable comes through wall from bathroom (or maybe down from ceiling) and runs along inside wall of airing cupboard, fixed to wall by clips, then into power shower pump. So not subject to movement or rubbing
Zerax, thank you for this. I have read and it does seem an electrician can use his judgment as there is no exhaustive detailed list of faults published. From the examples given I think that neither of the C2 faults listed by my electrician can be classed as C2 but may be C3. What can I do if this electrician is using his judgement inappropriately to get himself workThe OP may find this interesting... https://www.----------------------------/media/2149/bpg4-1.pdf
I can see that is often more trouble than many inspections warrant as pipe work can get in the way, needing disconnection, and many machines can be too heavy to safely move on your own. But that is not an excuse for coding it as a fault!Did he pull the washing machine out to test at the socket point? If not, why not?
Thank you. I emailed him 2 questions and here are his replies....The first thing you need to do is confront him. Remember Best Practice Guides although helpful are not the be all and end all it is down to an individuals judgement. I would be asking what factors he considered to warrant a Code 2 judgement and how this poses an urgent attention situation, if he cannot give valid reasons say you are going to lodge a complaint to the NICEIC and keep all correspondence to emails so you can use them.
[automerge]1601050422[/automerge]Of the cable in the airing cupboard is correctly supported throughout its length it’s not even a code.
Did he pull the washing machine out to test at the socket point? If not, why not?
Of the cable in the airing cupboard is correctly supported throughout its length it’s not even a code.
Did he pull the washing machine out to test at the socket point? If not, why not?
I wasn't there unfortunately but I don't think he pulled out machine or tested socket.Of the cable in the airing cupboard is correctly supported throughout its length it’s not even a code.
Did he pull the washing machine out to test at the socket point? If not, why not?
Thank you. I emailed him 2 questions and here are his replies....
ME: Regarding the washing machine, it's easy to pull it out or remove the non fixed little shelf unit next to it. Why is this dangerous. Why is it C2?
His reply: The access you are describing is not sufficient.
Me: What does shower cable need protecting from??
Reply : All cable below 2.4M in height need to be covered.
Incidentally, I actually had another electrician do an EICR a couple of weeks ago. He found neither of these issues!!!! He did advise changing a fuse and was going to come back to fix but unfortunately something serious happened to him shortly after before he came back or issued EICR. He is not working anymore, hence my need for this second electrician as I needed EICR for new tenancy.
[automerge]1601050308[/automerge]
[automerge]1601050422[/automerge]
I wasn't there unfortunately but I don't think he pulled out machine or tested socket.