EICR | on ElectriciansForums

Discuss EICR in the UK Electrical Forum area at ElectriciansForums.net

leep82

-
Arms
Joined
Nov 21, 2011
Messages
424
Reaction score
130
Location
Stoke on Trent
Ive recently mentioned on another thread of mine that when it comes to completing EICR's my experience is limited. I have my testing and inspection qualifications but have generally only used them to verify new work that i myself have installed, all relatively easy. At the minute I am sub contracting to a local company and tomorrow have to go and carry out an EICR on a pub. I was just hoping for any advice that anybody might be able to give me. Having spoken to some of the guys who already do this sort of work for him i dont feel that i will be anywhere near there speed. This wouldnt normally worry me as i would much rather take my time and be thorough but any advice/tips that could save me time or help me out would be most welcome
 
just do it:)

is nothing to worry about. as You told You've made some of new testing before , so when something will look different than You are expect , just check that with a "Book of Magic" (BS7671) :)
 
Don't panic, sometimes looking at a DB which isn't properly marked up can over awe you. Just look at it on a circuit by circuit basis.

Do a walk round first, note any observations as you go. Take in where there are switches, sockets, any other equipment.

If you can isolate the DB as a whole and turn on the circuits one at a time then do that. It's much easier to see what's on than what's not.

You know how to test obviously, you know what complies in terms of cable sizes, ocpd and disconnection times.

You'll be grand.
 
Just a heads up I have found that pup wiring is not the best as generally the landloards will get one of the locals in who once watched somone change a plug and thinks hes a spark, so unless it a nice new pub, I imagine you will be finding a lot of observations , and interesting installation methods :)
 
I carry out EICRs in pubs on a regular basis. I find best thing to do is start Cellar and work up, in the kitchens sometimes sockets will be on their own circuits instead of RFCs. Key to speed is Global IRs and keeping mental notes of what is there and not found yet. Wiring and add ons normally to a good standard as the brewery always do the testing and fine the landlords for ---- work.
 
Once again thanks for the replys. Im on an hourly rate not per circuit. My biggest concern is that i miss somthing. Im not sure how soon my current empmoyer thinks i can get this done, my previous employer who i worked direct to was very particular regarding testing and i like to think im pretty thorough. I dont know how big the pub is, if its occupied etc etc. Probably worrying over nothing. Quick question regarding r1 & r2 tests, been told a few different things by different people. For example just use a wander lead and test r2 or even just calculate it from my Ze/Zs readings
 
Once again thanks for the replys. Im on an hourly rate not per circuit. My biggest concern is that i miss somthing. Im not sure how soon my current empmoyer thinks i can get this done, my previous employer who i worked direct to was very particular regarding testing and i like to think im pretty thorough. I dont know how big the pub is, if its occupied etc etc. Probably worrying over nothing. Quick question regarding r1 & r2 tests, been told a few different things by different people. For example just use a wander lead and test r2 or even just calculate it from my Ze/Zs readings
r1 r2 and rn are end to end resistance readings of a RFC R1+R2 would be the combined resistances of a radial or lighting circuit Land cpc and the resistance of a RFC L and cpc once cross connected as per OSG GN3
 
Last edited:
Measuring R1+R2 is a means of calculating the maximum earth fault loop impedance of the circuit.
It also ensures that the earthing is continuous on the circuit.
The alternative to this, if the circuit has already been powered up, as it will have been on an EICR, is to confirm the earth continuity and the earth fault loop impedance by measuring Zs.
 

Reply to EICR in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Here the BPG#4 is useful, it is not a statutory document at all, but it provides good guidance as to what can reasonably considered as C1/C2/C3...
Replies
11
Views
1K
Yep They try to sell, sell, sell At the last asessment I told the asessor that I used SELECT to update my regs and inspection and testing, on...
Replies
6
Views
605

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top