So you are doing an EICR next year and you are inspecting a consumer unit with these 2 "makes" of RCBO's in it ...

[ElectriciansForums.net] EICR's after 1st Jan 2019 ....


So is it:
 
As from experience and manufacturers, direct information both the RCBO's are identical except for the printed livery on the casing so no code if it was a Hager and Wylex I would tend to say C3 improvement recommended especially if the incorrect RCBO was easily still purchasable.
 
The manufacturers of those two RCBOs have made a conscious attempt to differentiate them selves from each other by branding them differently.

It's not for the end user, installer or even inspector to jump to the conclusion that just because both manufacturers have used the same style of casing, which may well be made by the same manufacturer, that the product inside is exactly the same - I think I would struggle to form a decent court-worthy argument that the reg relates to the manufacturer of the casing and because they look similar the different brands can be ignored.
Substituting a product which looks similar but carries a less well known brand is almost always done for financial reasons and I think a judge or jury would be likely to pick up on that.

C3.
 
The manufacturers of those two RCBOs have made a conscious attempt to differentiate them selves from each other by branding them differently.

It's not for the end user, installer or even inspector to jump to the conclusion that just because both manufacturers have used the same style of casing, which may well be made by the same manufacturer, that the product inside is exactly the same - I think I would struggle to form a decent court-worthy argument that the reg relates to the manufacturer of the casing and because they look similar the different brands can be ignored.
Substituting a product which looks similar but carries a less well known brand is almost always done for financial reasons and I think a judge or jury would be likely to pick up on that.

C3.
Same manufacturer in the op picture but I agree with your comments regarding different brands used
 

Reply to EICR's after 1st Jan 2019 .... in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Here the BPG#4 is useful, it is not a statutory document at all, but it provides good guidance as to what can reasonably considered as C1/C2/C3...
Replies
11
Views
1K
  • Question
For the OP in case they have not come across them so far, the free BPG can be found here...
Replies
5
Views
570

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top