Yooj, Reckon you are on the money here. The DP main switch must have remained on in the panic.
I know from experience of running sub mains to Portacabin type class rooms with a PME origin.
I exported the earth. NIC made me insulate the earth and TT the classroom-there and then!
I am wondering whether the spark who did the work on the neighbours house was getting some funny readings when he was testing the installation due to a broken neutral (total supposition on my part however...we no more know it was a PME supply, than a broken neutral). He could well have removed the main earth that went to Momins house and the readings he was getting then could have potentially been ok...Again, supposition, and without seeing the install with my own eyes, then this is just a hypothesis. I will also hazard a guess that there is also continuity between Momin's and his neighbours pipework...maybe through a shared metallic gas and/or water supply pipework, which acted as the neutral return path due to a neutral supply break.
Some DNO's and in fact the IET (IEE) recommend that an earth spike can be installed on PME supplies to reduce the touch voltage on extraneouse metallic parts in the event of a neutral open-circuit supply side.
See attached file.
Exactly..This is the reason I want to know from the board. the fault was outside our house. Nothing in our house was faulty. the board gave 2 possibilities. Either (1) the underground cable was damaged. I hardly believe this and is very unlikely
Unlikely, yes...impossible no...Maybe this is the reason that the DNO do not want to dig up the old supply, as this could maybe prove that it was a broken neutral? I have heard of several cases of PME neutral breaks...some of which go undetected for years, since the consumers house has very good earthing properties from metallic services. These only came to light when utility supplies were changed to plastic, and thus effectively removing the return path.
or (2) the earth cable of ours which was next door is the cause because it was loose as admitted by the board. and as mentioned before the neighbour had some work done on 2 different occasions on his CU prior to the accident.
The likelyhood is that the big flash and bang when the DNO reconnected the earth was because there was a load on the main-earth due to a broken neutral. Reconnecting it just caused a flash-over arc.
Sorry to hear about your daughter's bad experience momin.
I've got one point:
whether this was a broken neutral/earth in a pme context, or a shared/looped earth between neighbouring dwellings, or both .... it's the DNO's responsibilty to provide an (external) earth path for every installation. If that path was broken due to a broken neutral then the liability is theirs; similarly, if an installation is without an earth path because it it shared with an adjacent installation and disconnected there (for maintenance or modification of that installation), it's still the DNO's responsibility.
Maybe a solicitor would be more appropriate than an electrician in this context.
The DNO will always maintain that its not their responsibilty to provide an earth if they do its out of good will. what a crock !
From the ESQCR:
**************************************
Equipment on a consumer's premises
24. - (4) Unless he can reasonably conclude that it is inappropriate for reasons of safety, a distributor shall, when providing a new connection at low voltage, make available his supply neutral conductor or, if appropriate, the protective conductor of his network for connection to the protective conductor of the consumer's installation.
Connections to installations or to other networks
25. - (1) No person shall make or alter a connection from a distributor's network to a consumer's installation, a street electrical fixture or to another distributor's network without that distributor's consent, unless such consent has been unreasonably withheld.
***************************************
24. states that the neutral/earth shold have been available...I bet this is why the DNO have now made sure that you have your own supply and earth. I would also be interested to know whether the DNO provided the neighbour with a new supply also.
25. As any electrician knows, touching DNO equipement is a no-no...However, how did the electrician working on the neighbours installation know that the earth which was disconnected, was actually the main earth for Momin's house. Was it suitably labelled? As far as he was concerned it was probably a redundant CPC or bonding conductor maybe. And as mentioned before, it might well have screwed up the test readings when connected, due to a broken neutral. Or, if there was not a broken neutral at the time of the work carried out, and it appeared to be just a redundant cable, then it might have just been left disconnected.
All the above adds up to nothing really, as it is just a hypothesis...however, the real questions that I would be asking, would be to the DNO in terms of why was the Main Earth to Momin's terminated in the neighbours house, and if there was a broken neutral, then both of these factors then were contributory to his daughters electrocution.
Yooj