I've been putting some new floor boxes in on am existing electrak system.
The floor boxes come pre-wired with 2x DSSOs and a data plate. There is also a 5m pre-connected steel flex conduit.
The flex and assembly is wired internally with 4mm singles.
The plug (taps in) is not fused so potentially this could see 4 x 13A, the track are off 40A MCBs.
Job was thrown on me late last night, told its all plug and play nothing to worry about.
Something didn't sit right with them, especially the four sockets on the 4mm singles, unfused.
I guess it comes down to whether the 4mm singles are protected by the 40A MCB, they are loose in 20mm steel flex conduit, sat on a concrete floor.
Probably not, thought I and obviously had no books to check CCC, so disconnected one of the sockets in each box.
Still not home yet, somewhere else not work, and wondering if I over reacted.
Back on Monday so no drama.
Just wondering if anyone has experience of this stuff.
The floor boxes come pre-wired with 2x DSSOs and a data plate. There is also a 5m pre-connected steel flex conduit.
The flex and assembly is wired internally with 4mm singles.
The plug (taps in) is not fused so potentially this could see 4 x 13A, the track are off 40A MCBs.
Job was thrown on me late last night, told its all plug and play nothing to worry about.
Something didn't sit right with them, especially the four sockets on the 4mm singles, unfused.
I guess it comes down to whether the 4mm singles are protected by the 40A MCB, they are loose in 20mm steel flex conduit, sat on a concrete floor.
Probably not, thought I and obviously had no books to check CCC, so disconnected one of the sockets in each box.
Still not home yet, somewhere else not work, and wondering if I over reacted.
Back on Monday so no drama.
Just wondering if anyone has experience of this stuff.