krissiboy
Hi all.
Still a bit new to this so here goes.
Just been called out to an electric central heating boiler. Customer says its been tripping the 40A MCB for a couple of months.- Not often but customer is a landlord and he doesn't want to lose his tenant over this.
Its fed with 10mm t+e cable via a 45a DP sw and is protected by a 30mA RCD. The rating of the boiler is 9kw. I tested the voltage a few times at the heater which came out to be between 236 and 240volts. So doin a bit of maths the current should be at worst 38.14Amps.
Using a clamp meter I found the current to be 40.4Amps. I suppose the circuit board would use a little power too hence the higher current.
Would this very small overcurrent be enough to trip the MCB albeit over a bit of time? I thought about trying a 45a MCB type B but they dont seem to make them for Hager Boards and I'm loathed to stick in a 50A.
So could I put in a 45Amp MCB of another make. Are there any other makes that are compatible with Hager?
Thanks in advance.
Still a bit new to this so here goes.
Just been called out to an electric central heating boiler. Customer says its been tripping the 40A MCB for a couple of months.- Not often but customer is a landlord and he doesn't want to lose his tenant over this.
Its fed with 10mm t+e cable via a 45a DP sw and is protected by a 30mA RCD. The rating of the boiler is 9kw. I tested the voltage a few times at the heater which came out to be between 236 and 240volts. So doin a bit of maths the current should be at worst 38.14Amps.
Using a clamp meter I found the current to be 40.4Amps. I suppose the circuit board would use a little power too hence the higher current.
Would this very small overcurrent be enough to trip the MCB albeit over a bit of time? I thought about trying a 45a MCB type B but they dont seem to make them for Hager Boards and I'm loathed to stick in a 50A.
So could I put in a 45Amp MCB of another make. Are there any other makes that are compatible with Hager?
Thanks in advance.