As said already just bond the supply end then it won't act in parallel with the internal cpc if you don't want it toI know armouring is ok as cpc on its own but I didn't know you could use both armouring and a core as a joint cpc
As said already just bond the supply end then it won't act in parallel with the internal cpc if you don't want it toI know armouring is ok as cpc on its own but I didn't know you could use both armouring and a core as a joint cpc
Earth rather than bond! No reason not to parallel them though.As said already just bond the supply end then it won't act in parallel with the internal cpc if you don't want it to
It's like being told of by the headmasterEarth rather than bond! No reason not to parallel them though.
only if you want to make the cooker TT.Question is, why wouldn't you parallel them up?
It's not always an option in every case.Question is, why wouldn't you parallel them up?