Hello, got an electric fire to fit, they want it on a switch. Only 2 sockets in room and 1 is a spur from the other, is there anyway i could use that supply?? Also wooden floor that they dont want taking up.

Thanks.
 
well, anymore than 3 kw puts you over a fused spur rating of 13 amp.

3000/230 = 13.04A

If i was doing the job than i would give it its own cct if there is room on the board.
use 20 A breaker and 20 A d/P switch for example?
Taking into account ref method for cable sizing? maybe best to find out the size of fire first?
just food for thought?
hope it helps?
 
Last edited by a moderator:
Thanks for the advice, will see what rating it is first but they want as least disruption as possible so own circuit may not be possible.
Thanks.
 
Change the supply to a fused spur,feed sockets one two and electric fire switch(just as well use another fused spur) off the supply fused spur

I would think,the 3Kw rated fire will take 12 ish amps rather than over 13, due to the supply voltage likely being greater than the 230 volt figure for load calculations

Better off with a lower rated fire though
No flexibility of installation = they get only whats possible rather than what may be wanted
 
fair comment about the supply being more than 230! old school rule of thumb!

3000/240 = 12.5 A

adding the fused spur as part of the ring main would comply with regs being stated as fixed eqpt, but fire cannot be more than 3kw, otherwise a dedicated cct would be req would you not agree.?

:)
 
Last edited by a moderator:

Reply to Electric Fire in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
330
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
975

Similar threads

The core tech was never Google. The core technology was Nest, and it’s sound. They got bought up by Google looking for a way in to the home tech...
2
Replies
27
Views
1K
J
The rcd spur being fitted is probably because there wasn't rcd protection of that supply.
Replies
5
Views
437

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top