Hi Guys, I've made this video (link below) to highlight an electric issue in my house. I wonder if any of you know what the issue is? I am going to call out an electrician but I would love to know your thoughts. Thank you for your time :) Ian
 
I’ve found that if you contact the DNO online and include the words ‘fire’ and / or ‘explode’ you get quite i quick response. N.B Not sayinging that’s an issue in this case. I had a problem with a faulty meter and was going round the houses with the supplier. Tried to contact them online and just added that I was scared that it was faulty and might catch fire. Funnily enough I got quite a quick response. Reckon they must have a key word filter on emails to prioritise. :D
 
Same fault I was called to with the disco shower. My video was slightly less professional...
Loose neutral on supply cable joint just outside the house.
I should also note that in this condition any earthed/bonded metalwork will have a voltage (possibly quite a tingly one) on it!
 
Last edited:
SC said 'loose connection' in the DNO's equipment in post #2 and I totally agree. A loose connection in the service cable joint for example. But others have gone on to be more specific by saying it's the neutral. Why? What evidence do we have that the neutral is faulty and not the line?

We've had a discussion with lots of good ideas about why high resistance connections are (thought to be) more common in neutrals, specifically in domestic installation work. Explanations include sparks habitually wiring the line first, then doing the neutral with waning concentration; or manufacturers using terminals of inferior design in CU neutral bars, etc. But does this apply to DNO equipment too, such as service cable joints? Where CNEs are terminated they have to be extra vigilant about continuity, so I'd almost expect a higher rate of failure in line connections.

Thoughts?

OP: I'd call the DNO. The problem is theirs, not yours, the meter display showing 'Low U' is a dead giveaway.
 
SC said 'loose connection' in the DNO's equipment in post #2 and I totally agree. A loose connection in the service cable joint for example. But others have gone on to be more specific by saying it's the neutral. Why? What evidence do we have that the neutral is faulty and not the line?

Have seen it happen a couple of times on my local estate alone, and both times I have spoken to the network guys and they confirm it is a common thing, mainly on joints from the 1970s. Didn't ask them their thoughts on why neutral, but wish I had now just out of interest!

Both times the symptoms were the same (flickering lights when other loads switched on, raised voltage on exposed metalwork, etc.).
 
100% is upstream of Meter as already said so it's the DNO issue to resolve. Could be line or neutral but frankly who cares at this stage......call the DNO and report it.

Awesome video OP :)
 
SC said 'loose connection' in the DNO's equipment in post #2 and I totally agree. A loose connection in the service cable joint for example. But others have gone on to be more specific by saying it's the neutral. Why? What evidence do we have that the neutral is faulty and not the line?

We've had a discussion with lots of good ideas about why high resistance connections are (thought to be) more common in neutrals, specifically in domestic installation work. Explanations include sparks habitually wiring the line first, then doing the neutral with waning concentration; or manufacturers using terminals of inferior design in CU neutral bars, etc. But does this apply to DNO equipment too, such as service cable joints? Where CNEs are terminated they have to be extra vigilant about continuity, so I'd almost expect a higher rate of failure in line connections.

Thoughts?

OP: I'd call the DNO. The problem is theirs, not yours, the meter display showing 'Low U' is a dead giveaway.

Not necessarily the joint in the cable where the neutral fails being more common.

However further back to the transformer sees quite often the star point connection failing, especially on smaller transformers.

Most DNOs as standard are fitting K Type transformers now with a 200% FLC rated star point connection.

These are failing due to the sharp increase of harmonics being put onto our distribution network.
 
Hi Rob! That's something beyond my area of expertise .... What is a "K Type transformer?" Or are you just saying it's a tx rated for a K factor of 2?

A "K-Type" Transformer is a generic name used for a transformer that are designed to reduce the heating effects of harmonic currents. The K-factor rating is an index of the transformer's ability to withstand harmonic content while operating within the temperature limits of its insulating system.

The ones I have seen the DNO fit, and a few I have overseen installed, along with better quality insulation, offered a greater sized star point connection. (200% greater than the phases).

Because of the phase angle change by the transformer (most DNO transformers supplying LV have a DYn11 vector group). Harmonics can not pass through to the primary side. An thus the transformer needs to take the brunt of it.
 

Reply to electric meter issue. The grid, meter or consumer unit issue? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
733
If two tariffs are sufficient, and you don't need too many ways, you can easily add an SPD kit to the Fusebox F2014DT dual tariff board. The only...
Replies
1
Views
318

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top