B
Boberto
Had a text from a customer I did some work for last November. Message was that both the lady and her husband have had slight electrical shocks from "metal bits" in her kitchen. I asked "what metal bits?" and they responded by saying the dishwasher, oven and hob etc. The oven is on its own dedicated circuit. The other appliances are connected to the ring. They mentioned they only experience it when bare footed.
The modifications carried out in November included extending the kitchen ring to allow for a few more socket outlets and extend lighting circuit to allow for pelmet lighting. Installation is TT. ZE, ZS, IR all fine on testing. RCD tested fine. Main equipotential earthing conductors in place.
Got to go up there tomorrow to sort it out. Not something I have experienced before after my own work. Only people still working there after I finished were the tiler who was going to loosen some socket fronts off to tile behing and fix them back himself. And the plumber doing some modifications the the pipe work.
Suggestions where to start ?
The modifications carried out in November included extending the kitchen ring to allow for a few more socket outlets and extend lighting circuit to allow for pelmet lighting. Installation is TT. ZE, ZS, IR all fine on testing. RCD tested fine. Main equipotential earthing conductors in place.
Got to go up there tomorrow to sort it out. Not something I have experienced before after my own work. Only people still working there after I finished were the tiler who was going to loosen some socket fronts off to tile behing and fix them back himself. And the plumber doing some modifications the the pipe work.