Been asked to make previsions for elec shower in a future outbuild in garden of house I am starting to rewire tomorrow.

The house itself will be heated by central heating- all lights led etc just 1x induction hob then a fan oven +MW. so no excessive load in the house.

Head is 100a SP in external meter box- and c/u in house is >3m so will need to fit a switch fuse isolator switch in the external meter box then 25mm 3c swa from box to c/u.

My question is for the outbuilding supply- theres no space in the meter box for a 2nd switch fuse isolator for the outbuilding so will have to come off of an upfront mcb in the house c/u. But if there wanting like a 9kw shower plus a handful of sockets/lights/heater down there- thats looking at 25/35mm 3core at a 35meter run- which i think is pretty excessive.

1)Has anyone ever fitting a shower at such a distance in for example an outbuilding
2)does the isolator for the house >3m swa tails need to be fused or can it just be a 100a dp main switch? (i think the answer to my question is yes as I can't rely on the dnos mains head fuse- but space looks tight and I know them wylex fused isolators are quite bulky!)
 
would take the builder about half an hour to cut in a recessed box and cost about ÂŁ30 to buy.with this you could house a switch fuse for the house and another for the outbuilding. In the existing you could install something like a rec 2 for a single point of isolation. Much better than having to run the SWA internal and also having the distribution circuit on a circuit breaker where you will struggle to achieve any discrimination... just my thoughts.
like this idea lee thanks!
going to ask the builder to cut a 2nd meter box in and run 2x 32mm pipes between.

then fit a 100a rec switch after the meter- then into a henley (in the 1st meter box)

then 2 sets of 25mm tails through the pipes into the 2nd meter box

hopfully 2x of these will fit side by side:
Wylex 100A Domestic Switch Fuse Unit - http://www.screwfix.com/p/wylex-100a-domestic-switch-fuse-unit/5290J?kpid=5290J&gclid=CM6_4P3cytQCFc2d7QodAP0FJg&gclsrc=aw.ds&dclid=CJHY__3cytQCFWmnUQodOrQIRw

have a 63a isolator with 35meters of 16mm going to the future outbuilding
and a 80a isolator with 10meters of 16mm supply the house c/u
 
like this idea lee thanks!
going to ask the builder to cut a 2nd meter box in and run 2x 32mm pipes between.

then fit a 100a rec switch after the meter- then into a henley (in the 1st meter box)

then 2 sets of 25mm tails through the pipes into the 2nd meter box

hopfully 2x of these will fit side by side:
Wylex 100A Domestic Switch Fuse Unit - http://www.screwfix.com/p/wylex-100a-domestic-switch-fuse-unit/5290J?kpid=5290J&gclid=CM6_4P3cytQCFc2d7QodAP0FJg&gclsrc=aw.ds&dclid=CJHY__3cytQCFWmnUQodOrQIRw

have a 63a isolator with 35meters of 16mm going to the future outbuilding
and a 80a isolator with 10meters of 16mm supply the house c/u
sounds good to me.
 
Personally, I would consider not putting one of them 'instant' heat shower in the outbuilding.
Instead, have a look at one of the smaller unvented direct hot water tanks (Megaflo, etc) with an immersion heater. A 70litre or 125litre tank should be plenty big enough.
Your electrical current requirement for the shower then plummets to 3KW. Its also easy then to add other hot water items, like a wash-basin.
 
Why not use a smaller switchfuse like a KMF unit, if the meter gets changed for a digital one you might get two in the same meter box.


I'm curious as to what people would think about having only one distribution circuit which feeds both the house and the outbuilding?
 
What about a 80A 3 phase switch-fuse in another meter box next to one with meter/cut out or if you think that after diversity the demand will be no more than 50A from house consumer unit.
 
Last edited by a moderator:
I can kind of see where you're going with this, but I'm not sure you'll get one small enough to fit in a meter box sensibly.
Plus I don't like the idea of a metal switchfuse in a meter box which doesn't really provide much in the way of waterproofing
100A Eaton Glasgow (reduced fuse size) but all depends on if after diversity the outbuilding can come off house consumer unit on 50A mcb
 
100A Eaton Glasgow (reduced fuse size) but all depends on if after diversity the outbuilding can come off house consumer unit on 50A mcb

In my xperience they go rusty rather quickly in damp environments like this.

I thought when you said TP switchfuse you were suggesting using the L1 fuse for the house and the L2 fuse for the outbuilding, I can't see why you'd want a TP one otherwise on a single phase supply.
 
In my xperience they go rusty rather quickly in damp environments like this.

I thought when you said TP switchfuse you were suggesting using the L1 fuse for the house and the L2 fuse for the outbuilding, I can't see why you'd want a TP one otherwise on a single phase supply.
TP and switched N and yes fuse for L1 and L2 I take the point of if in a damp environment .I think Legand do a IP enclosure with din rail and have DP switches and fuse holders could be an idea
 
TP and switched N and yes fuse for L1 and L2 I take the point of if in a damp environment .I think Legand do a IP enclosure with din rail and have DP switches and fuse holders could be an idea

Personally I wouldn't be trying to reinvent the wheel, KMF switchfuses fit nicely in a meter box alongside the meter etc, so will be fine with two in an empty meter box.
 

Reply to electric shower in outbuilding in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
830

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
487
  • Question
How did it go?
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top