Been asked to make previsions for elec shower in a future outbuild in garden of house I am starting to rewire tomorrow.

The house itself will be heated by central heating- all lights led etc just 1x induction hob then a fan oven +MW. so no excessive load in the house.

Head is 100a SP in external meter box- and c/u in house is >3m so will need to fit a switch fuse isolator switch in the external meter box then 25mm 3c swa from box to c/u.

My question is for the outbuilding supply- theres no space in the meter box for a 2nd switch fuse isolator for the outbuilding so will have to come off of an upfront mcb in the house c/u. But if there wanting like a 9kw shower plus a handful of sockets/lights/heater down there- thats looking at 25/35mm 3core at a 35meter run- which i think is pretty excessive.

1)Has anyone ever fitting a shower at such a distance in for example an outbuilding
2)does the isolator for the house >3m swa tails need to be fused or can it just be a 100a dp main switch? (i think the answer to my question is yes as I can't rely on the dnos mains head fuse- but space looks tight and I know them wylex fused isolators are quite bulky!)
 

Reply to electric shower in outbuilding in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
829

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
487
  • Question
How did it go?
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top