Electric shower pull switch isolator | Page 5 | on ElectriciansForums

Discuss Electric shower pull switch isolator in the UK Electrical Forum area at ElectriciansForums.net

Joined
Mar 12, 2011
Messages
191
Reaction score
31
Location
Ayr
Hi, my neighbour has had to change his electric shower (6kw) pull switch (32A) 3 times in 4yrs. Apart from it possibly being poor quality switches he,s replacing, I was wondering if there is any reason not to leave the pull switch isolator in the "on" position. Thanks
 
Another vote for the Crabtree 50 amp.
Superb. I pretty much insist on them after being called to a house after a fire brigade call out to a very much burnt out 45 amp switch. So I put a Crabtree in. The best I could get the shower to pull was 40 amp and all the connections were very secure in the old switch - so why did it burn out? So yeah - now I go for that extra ‘comfort margin’ - very little faith in anything else.
 
Another vote for the Crabtree 50 amp.
Superb. I pretty much insist on them after being called to a house after a fire brigade call out to a very much burnt out 45 amp switch. So I put a Crabtree in. The best I could get the shower to pull was 40 amp and all the connections were very secure in the old switch - so why did it burn out? So yeah - now I go for that extra ‘comfort margin’ - very little faith in anything else.
[/QUO
 
If the conductors show no sign of thermal damage you can probably rule out poor terminations. In my opinion even a poor quality pull switch shouldn't really fail with a 6kw shower although you couldn't rule this out. If they are not switching this under load you can rule this out so this leaves other influences, this could be environmental such as moisture from steam or an issue with the shower itself. To rule out the switch I would fit a quality accessory such as already mentioned, Crabtree.
 
Although I agree that the Crabtree switches are very good and make terminating even 10mm cable much easier they do need fixing to the underside of a truss or similar with the way the feed and load cables come through seperate entries, so IMO not always ideal as a replacement.
The Click 50a pull switch is a good alternative, never had one fail yet and they have double screw terminals.
 
Although I agree that the Crabtree switches are very good and make terminating even 10mm cable much easier they do need fixing to the underside of a truss or similar with the way the feed and load cables come through seperate entries, so IMO not always ideal as a replacement.
The Click 50a pull switch is a good alternative, never had one fail yet and they have double screw terminals.

I know what you mean. I’ll have a look at those - I’ve not used one yet. It’s good to talk. Thankyou.
 
Although I agree that the Crabtree switches are very good and make terminating even 10mm cable much easier they do need fixing to the underside of a truss or similar with the way the feed and load cables come through seperate entries, so IMO not always ideal as a replacement.
The Click 50a pull switch is a good alternative, never had one fail yet and they have double screw terminals.
Only usually needs a small bit of wood putting in the ceiling above. Not too much trouble, but I know what you mean.
 
Everyone calmed down a little?

8 quid for a shower pull switch is a sign that it’s not very good quality. Coupled with some customers rough treatment of yanking the pull cord because it doesn’t always click on... (because it’s been yanked once too often in the past!)

Fit quality. Fit once. Forget
 
Yes, totally agree, I only wanted confirmation by my peers that it would be ok to leave isolator on mostly, to cut down on yanking. But do realize a good quality switch should be able to handle that. But thanks to the main body of the kirk for all advice ;)
 
Yes, totally agree, I only wanted confirmation by my peers that it would be ok to leave isolator on mostly, to cut down on yanking. But do realize a good quality switch should be able to handle that. But thanks to the main body of the kirk for all advice ;)

Just don’t spend too much time in there yanking away ;)
 
Yes, totally agree, I only wanted confirmation by my peers that it would be ok to leave isolator on mostly, to cut down on yanking. But do realize a good quality switch should be able to handle that. But thanks to the main body of the kirk for all advice ;)

As a electrician what consequences do you expect that makes this question valid
 

Reply to Electric shower pull switch isolator in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Better off with the click prw213 as it has twin screw termination.
Replies
9
Views
986
I thought that too, but I didn’t want to upset the old fella by telling him 😛
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top