The machine install itself will still be subject to testing albiet via the relevant BS60204, when the controls are energised after install and dependent on the machine design and layout as to what requires testing the Annex A of the BS60204 explains all the required testing procedures and confirmations and yes it does somewhat mimic the BS7671 in some of its wording or vice versa (chicken or egg).

On installation you still have to ensure the integrity of the electrical system you have just fitted again the extent of your testing is subject to machine/control design, exemptions do exist - Where the calculations of the fault loop impedance or of the resistance of the protective conductors are available and when the arrangement of the installation permits the verification of the length and csa of the conductors, verification of the continuity of the protective conductors can replace the Zs measurement.

Even having motors running of drives where you cannot do a practical measurement then you will still need to confirm the continuity of the protective conductor.

If you are as in the OP situation installing a machine line then it would almost definately be subject to required testing procedures if the OP expresses these are not been carried out then the installers or those commisioning the production line are not doing what is required to sign the system over.
 

Reply to Electrical testing on Machines in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
850

Similar threads

You may still have a problem with earth leakage though, it could be that the Samsung has less leakage than the Bosch ones. If you do get a random...
Replies
13
Views
2K
  • Question
Hi Just catching up on some threads. Did you get sorted out for your course? If you are on one now you can apply to join our trainee forum Apply...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top