Exactly,why wouldn’t you Main bond & DB , with TTI bet as soon as power is down there an outlet will be put in. So I'd be trying for a small local board and TT.
If it could be used to supply class I equipment or had any exposed conductive parts then you would need to consider adding the surrounding area to the equipotential zoneWhat would happen if a power point was added in the barn?
Well, you certainly wouldn't do both if you're talking about bonding to the incoming supply, but cost would be the obvious reason. Someone asks for one outside light, they may want the most economical quote so they may have questions if they are quoted for a rod and a db on top of the swa and the light itself.Exactly,why wouldn’t you Main bond & DB , with TT
Exactly,but what actually compliesIf it could be used to supply class I equipment or had any exposed conductive parts then you would need to consider adding the surrounding area to the equipotential zone
Well, you certainly wouldn't do both if you're talking about bonding to the incoming supply, but cost would be the obvious reason. Someone asks for one outside light, they may want the most economical quote so they may have questions if they are quoted for a rod and a db on top of the swa and the light itself.
Well bs7671 isn't statutory anyway despite my earlier flippant comment, but in terms of h&s acts and electricity at work etc which are, you need to look at what's present. In my opinion short of encasing the light in a locked or screwed cabinet with adequate signage you're creating an unacceptable risk if there's any touchable metal with a low resistance to true earth at the same time as the light. Therefore i would personally say it is not safe if that is the case. This would be even more so if the area was used by the general public and was within reach at ground level, and was on a TN-C-S service.Exactly,but what actually complies
Hi All - apologies if I was a bit short on my reply. If I understand correctly, my thought was this is a special location under section 705. And so if ADS is in use TNC is prohibited by regulation 705.411.4, which leads me to TT. Bonding could then be done locally locally to that building's earth terminal, rather than having to take it back to the site cut out. Or have I misunderstood?Exactly,why wouldn’t you Main bond & DB , with TT
things could be plugged in....the grass would get cut, the dead leaves blown next door, that dreadful leandi would be cut down, the list goes onandonandon.What would happen if a power point was added in the barn?
…...as long as an rcd didn't trip, that is. Mind you...…..?things could be plugged in....the grass would get cut, the dead leaves blown next door, that dreadful leandi would be cut down, the list goes onandonandon.
Agree,I would of preferred a local DB @the said building,then main bonding could take place with the TT system created.Hi All - apologies if I was a bit short on my reply. If I understand correctly, my thought was this is a special location under section 705. And so if ADS is in use TNC is prohibited by regulation 705.411.4, which leads me to TT. Bonding could then be done locally locally to that building's earth terminal, rather than having to take it back to the site cut out. Or have I misunderstood?