Hey all, quick question for you.
Did an earth loop at a socket, got 20 ohms which is acceptable as it's on an rcd.
Did another earth loop on a soft test at a light fitting using a long lead l/n at socket and connected to earth at light. The lighting circuit not being on an rcd.
Got 20 ohms again?
Am I reading through the socket circuit by using this method? I would presume I'm testing the earth at the light back to the board and so on but I'm confused as to how I got the exact same reading? This reading not being acceptable if it's not on a rcd.
Any ideas welcome, thanks