ELI at pendant..using long lead | Page 2 | on ElectriciansForums

Discuss ELI at pendant..using long lead in the Australia area at ElectriciansForums.net

C

claire_r

Hey all, quick question for you.

Did an earth loop at a socket, got 20 ohms which is acceptable as it's on an rcd.

Did another earth loop on a soft test at a light fitting using a long lead l/n at socket and connected to earth at light. The lighting circuit not being on an rcd.

Got 20 ohms again?

Am I reading through the socket circuit by using this method? I would presume I'm testing the earth at the light back to the board and so on but I'm confused as to how I got the exact same reading? This reading not being acceptable if it's not on a rcd.

Any ideas welcome, thanks :)
 
The main reason i haven't bought them, is that i not yet got into a situation where i've thought 'i wish there was some gadget that would make this easier'.

Thats the trouble with you young'uns. Always want the easy way!
:D
 
I like coffee, I'm gettin some....:D
ffffffff

Yeah, I've made my own adaptors for "kliks" and the like, just put a single socket in the other end of the plug flex.
even better.
the kit looks good though---dunno about the 55 quid mind.
There are so many variations though,that aren't covered,such as those gu 10's that only take cfls(sgu10 i think they're called),Ges,pl etc.
One of the meters I had been using a little while back had a adapter on the earth probe that you could plug in your N probe,which gave you a spare hand to hold onto your steps.Your test is between phase and earth.
(croc clip on earth)
 
Last edited:
lol well thanks all for suggestions....hmm i might have to have a looky into the plug in adapters...make my life alot easier as yet again today.....eli at a pendant....did it the old fashioned way though....wish i had pointier elbows to press the test button hehe.
 

Reply to ELI at pendant..using long lead in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
698
davesparks
D
Ok I’ll try this when I’m down
Replies
4
Views
398

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top