Crosswire

OK,
Settle this once and for all please chaps.

When keying off emergency lights, should you switch;

1) just one pole (e.g. the permanent live)
2) two poles ( e.g. both switched and permanent lives)

or

3) three poles ( both lives and neutral also (as some key switches have two poles) ) ?


Thanks
 
Last edited by a moderator:
Anyway,
back to original point - seeing as no-one has disagreed can I safely assume that only the permanent live is to be switched via an key switch for testing purposes?

yes you switch the perminant live

the emergency lights have a perminant live feeding them so the battery packs charge, you switch this to cut the power to them and the battery will kick in

switch the permiant live,
if you switched the switch live, they wouldnt work properly and you should never swicth the neutral
 
Last edited by a moderator:
Anyway,
back to original point - seeing as no-one has disagreed can I safely assume that only the permanent live is to be switched via an key switch for testing purposes?

yes you switch the perminant live

the emergency lights have a perminant live feeding them so the battery packs charge, you switch this to cut the power to them and the battery will kick in

switch the permiant live,
if you switched the switch live, they wouldnt work properly and you should never switch the neutral

unless you get jobs from MY HAMMER in which case anything goes!!!:eek:
 
i use black as permanent feed and brown as switch wire

also if you use crabtree klik roses ( which i use all the time) the pre wired plug tops for the 4 pin kliks have brown in the L terminal and black in the A terminal,

so then it all matches each other up.
 
the sw live and and perm live are both brown, imho...the switch live tagged for id only. I've always used dp key switches, cuts both supply and sw/l....thats how i've allus done it.

when red was red, line, the same, all lives were red, switched or otherwise...tagged with yellow ferrals/tape for id only.

Only deviations were 3-phase, if on yellow phase for instance, yellow feeds and yellow sw tagged...bloody black? switch wires.Brussels needs bombing -;)
 
you should never switch the neutral....lol
no YOU SHOULDN'T

many em lighting circuits are double pole, in fact some key switches say N in, N out, L in, L out ...just in case
Some switch both perm live and the s/w, again dp


I best not try to explain why sometimes dp em key switches are used
 
AND no, you do not only switch the perm live, the key switch cuts all power including sw's to the fitting, or sometimes a complete circuit and importantly line/s and neutral. If a large circuit you will need a contactor.
 
the sw live and and perm live are both brown, imho...the switch live tagged for id only. I've always used dp key switches, cuts both supply and sw/l....thats how i've allus done it.

when red was red, line, the same, all lives were red, switched or otherwise...tagged with yellow ferrals/tape for id only.

Only deviations were 3-phase, if on yellow phase for instance, yellow feeds and yellow sw tagged...bloody black? switch wires.Brussels needs bombing -;)

we are talkin about 3 core cable which has black grey and brown, if wiring in singles then yes permanent live or not it would be brown. but if using 3 core cable which colour to use a permanent brown or black? thats the debate .:)
 
we are talkin about 3 core cable which has black grey and brown, if wiring in singles then yes permanent live or not it would be brown. but if using 3 core cable which colour to use a permanent brown or black? thats the debate .:)

But either way it has to be reidentified brown.
 
istock_can-of-worms.jpg
 
i use black as permanent feed and brown as switch wire

also if you use crabtree klik roses ( which i use all the time) the pre wired plug tops for the 4 pin kliks have brown in the L terminal and black in the A terminal,

so then it all matches each other up.
That's my reason for doing it; while I agree with the 'switch principle' (as in using sleeved blue as switched line) this is the way manufacturers have decided it is done and it is easier to go with the flow than against the grain - sure you could rewire all the plugs for the sake of making a point, but I'd rather just accept that that's the way it's done.
 
That's my reason for doing it; while I agree with the 'switch principle' (as in using sleeved blue as switched line) this is the way manufacturers have decided it is done and it is easier to go with the flow than against the grain - sure you could rewire all the plugs for the sake of making a point, but I'd rather just accept that that's the way it's done.

Wish mine came pre-wired :(
 
AND no, you do not only switch the perm live, the key switch cuts all power including sw's to the fitting, or sometimes a complete circuit and importantly line/s and neutral. If a large circuit you will need a contactor.
You can do it like that, or you could just switch the permanent live so all the non-emergency lights stay on when you do the emergency lighting test and the people working in the office don't start freaking out because all the lights have gone off.
 
You can do it like that, or you could just switch the permanent live so all the non-emergency lights stay on when you do the emergency lighting test and the people working in the office don't start freaking out because all the lights have gone off.


This is the main point, and I agree. However if you don't do this you won't know if the the emergencies give adequate lighting in the event of a power cut.

Damned if you etc....

Think I'll stick to just permanents and save myself the grief:)

(P.S. You should never switch ONLY the neutral. If you break ALL live conducters (including neutral) the switch is now an isolator).
 
Last edited by a moderator:
if you don't do this you won't know if the the emergencies give adequate lighting in the event of a power cut.
I would argue that that is the job of the designer - in most situations as far as the guy testing the emergency lights is concerned he just needs to look out for the lights coming on where the LEDs have gone out, then check the LEDs have come on again when power is restored.
 

Reply to Em Lighting key switches! in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
132
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
914
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
Double pole switches? Mounted on a grid module? Ignore the fact they have a N stamped on them. Or is your 2 gang switch decorative, and you...
Replies
3
Views
771
Yes I understand the setup now. Sorry about my confusing first post 🫢 It might be worth buying the Livolo switches you identified and lash at...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top