Deswin. Let us start at the beginning because I am confused about what you have and have not changed.
I have attached below two clear pictures of how to connect up the grey
Power Supply Control to the
FOSA RFID card reader. I suggest you carefully check this is how
you have connected the reader, the push and the power supply control together.
You cannot power both EM locks directly from the RFID reader or the Control Power Supply. Each lock needs its own power supply - the ones you sent a picture of which have a metal cover with many holes for ventilation.
You connect the locks as you have shown in your message #23 using the contacts of the relay (common and NO) to switch the power to them on and off. When this relay is energised the common is connected to the Normally Open (NO) contacts which switches power from the 12V dc 36W power supply to its lock.
This relay (Plasma) is controlled - the coil is connected to - the Common and NC contacts of the Power Supply Control. This will mean power is sent to the relay until the RFID key reader is activated - when the reader is activated the Power Supply Control contacts NC open. This turns off the relay which in turn turns of the EM locks. The relay is turned off for a time set on the Delay screw of the Power Supply Control.
All 3 power supplies should be set to output 12V dc.
Be careful to wire the relay coil correctly because it has a light inside it - an LED - to indicate when the relay coil is energised. The + of the coil must connect to the NC terminal on the Power supply control and - to the COM terminal.
The wire for the lock circuits must be thick like the brown and blue wires shown in your picture in # 25. The wires for the RFID reader, door push and relay coil can be thin.
The EM locks have + and - connections which must be connected so + goes to the Plasma relay and - goes to the 0V/Gnd of its power supply.
if you have new EM locks and connected everything together as in the diagrams and as I have described then it should work.
Your meter does have a resistance setting - please do as I have asked and measure the resistance of the EM locks at the lock terminals and then do the measurement at the end of the cable where is connected to the Plasma relay - disconnected from the relay but connected at the lock end. The four readings should be the same. Tell me what you measure and how you measured.
[automerge]1575928685[/automerge]
power supply control wiring diagram - Google Search - https://www.google.com/search?rlz=1C1GCEA_enGB822GB822&biw=1517&bih=694&tbm=isch&sxsrf=ACYBGNSQMqzRr3ZlbPWqRpk5pFTOB8ibTw%3A1575928590851&sa=1&ei=DsPuXb3PM6HaxgPf5rWADQ&q=power+supply+control+wiring+diagram&oq=power+supply+control+wiring&gs_l=img.1.0.0j0i8i30l3.23477.28363..33273...0.0..0.168.2352.28j2......0....1..gws-wiz-img.......35i39j0i24j0i30j0i5i30.2Sy1fBQG7-E#imgrc=FKujQGpBOxTnvM:
[/QU
This morning i go again there and measure the resistance of the both emlock. The first emlock resistance is 30 ohm and the second em lock resistance is 24 ohm. The first em lock voltage is 12.7VDC and the second em lock 11.79VDC when both power ON. I use this wiring diagram for RFID wiring system but still the first emlock works perfectly than the second em lock.
View attachment 54487
The exit push, ring bell, wireless remote, and the RFID access card all works fine with the power supply i used with i show you diagram in #37. Before that the shop i done wiring has one aluminum frame glass door equip with one magnet and works fine.
After the shop owner change mind and install two door frameless swinging glass door and install with two magnet then i did some changes in the wiring where i add another relay to control two em lock and two emlock with individual power supply. Still the first em lock works but the second emlock didn't work.
Deswin. Let us start at the beginning because I am confused about what you have and have not changed.
I have attached below two clear pictures of how to connect up the grey
Power Supply Control to the
FOSA RFID card reader. I suggest you carefully check this is how
you have connected the reader, the push and the power supply control together.
You cannot power both EM locks directly from the RFID reader or the Control Power Supply. Each lock needs its own power supply - the ones you sent a picture of which have a metal cover with many holes for ventilation.
You connect the locks as you have shown in your message #23 using the contacts of the relay (common and NO) to switch the power to them on and off. When this relay is energised the common is connected to the Normally Open (NO) contacts which switches power from the 12V dc 36W power supply to its lock.
This relay (Plasma) is controlled - the coil is connected to - the Common and NC contacts of the Power Supply Control. This will mean power is sent to the relay until the RFID key reader is activated - when the reader is activated the Power Supply Control contacts NC open. This turns off the relay which in turn turns of the EM locks. The relay is turned off for a time set on the Delay screw of the Power Supply Control.
All 3 power supplies should be set to output 12V dc.
Be careful to wire the relay coil correctly because it has a light inside it - an LED - to indicate when the relay coil is energised. The + of the coil must connect to the NC terminal on the Power supply control and - to the COM terminal.
The wire for the lock circuits must be thick like the brown and blue wires shown in your picture in # 25. The wires for the RFID reader, door push and relay coil can be thin.
The EM locks have + and - connections which must be connected so + goes to the Plasma relay and - goes to the 0V/Gnd of its power supply.
if you have new EM locks and connected everything together as in the diagrams and as I have described then it should work.
Your meter does have a resistance setting - please do as I have asked and measure the resistance of the EM locks at the lock terminals and then do the measurement at the end of the cable where is connected to the Plasma relay - disconnected from the relay but connected at the lock end. The four readings should be the same. Tell me what you measure and how you measured.
[automerge]1575928685[/automerge]
power supply control wiring diagram - Google Search - https://www.google.com/search?rlz=1C1GCEA_enGB822GB822&biw=1517&bih=694&tbm=isch&sxsrf=ACYBGNSQMqzRr3ZlbPWqRpk5pFTOB8ibTw%3A1575928590851&sa=1&ei=DsPuXb3PM6HaxgPf5rWADQ&q=power+supply+control+wiring+diagram&oq=power+supply+control+wiring&gs_l=img.1.0.0j0i8i30l3.23477.28363..33273...0.0..0.168.2352.28j2......0....1..gws-wiz-img.......35i39j0i24j0i30j0i5i30.2Sy1fBQG7-E#imgrc=FKujQGpBOxTnvM:
On the other hand, i tried using power supply 12VDC 5A to both emlocks but still the second one didn't work fell even the magnet is still new. Like as i said I did wiring for each power supply and did connect V+ to + and V- to - from power supply to em lock. And still the second emlock fail to work.