stevels4
-
Am I missing something here ? Where is the live feed to the meter, I can see the neutrals in and out and the live out only.
You have a 3 phase cut out but this is supplying 3 single phases so cannot be reassigned for a 3 phase supply.
You could be looking at a new 3 phase service being installed by the DNO and that will certainly take weeks to organise and blow the budget!
You have a 3 phase cut out but this is supplying 3 single phases so cannot be reassigned for a 3 phase supply.
You could be looking at a new 3 phase service being installed by the DNO and that will certainly take weeks to organise and blow the budget!