Good afternoon,

yesterday we had a power cut in our care home, 2 emergency lights did not kick in. They kick in on the key flick test which i do every month but they do not kick in when i switch off the MCB in the consumer unit. We have just had new batteries put in and they are fully charged. The green led is on when the power is on. We do have a contract for maintenance with Lowe and Oliver but as maintenance manager if i can fix it it will save the call out fee. Any ideas why they would work on a flick test but not a full power cut?
 
I am just wondering if you are quickly flicking them on with the test facility to verify operation but when you turn off the breaker there is sufficient time getting to the fittings from the board for them to fail in other words they briefly illuminate and then fail.
 
The lights illuminate when the test switch is operated.
The lights do not illuminate when power to the entire installation is lost, ie. a power cut.

That is not likely to be caused by the lights being fed from a different circuit.

My guess would be that the test switch is incorrectly wired so that it is connected to the switched live terminal thus switching the light on rather than simulating a power failure.
If this is the case then it probably doesn't have an unswitched supply at all and so the battery hasn't been charged.
 
Depending on where the board is they may illuminate for a short period then have failed by the time he gets there. He may only be flicking the test facility quickly but need more info and he seems to have gone.
 
The OP doesn't say explicitly that the charge indicator goes off when the test switch is operated, only that it did when the supply was pulled. The only consistent explanation seems to be Davesparks'...
 
It's seems unlikely if they have new batteries, but of course is not impossible.
May have replaced batteries due to previous failure when in fact that wasn't the issue, like you say maybe no permanent supply or the fiitings have duff charging parts.
 

Reply to Emergency lighting help in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
270
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
764

Similar threads

Fitted a lot of this sort of light recently, with all tests reporting back through central Dali controller(s).
2
Replies
15
Views
941
nicebutdim
N
It’s getting to the point where full LED replacement is cheaper than spending time on testing and possibly replacing parts.
Replies
6
Views
752

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top