Resetting the safety relay (e-stop circuit) must only allow re-start, not implement re-start.
The start function is not a safety function.
The stop/e-stop MUST override the start function.

Not sure what you mean by the way you are looking at the outputs of the safety relay.

Why would you have 3 devices to start?
Blue to reset, yes.
Green to start not acceptable under BS4163, key switch required, key switch can be used as a start under other standards. Both must be momentary.

A conventional stop button would not be part of the safety function, so, if there was an incident requiring e-stop and witnessed at the start location then an e-stop would be required.

These things are not the sort of thing that you can "get" over internet forums, you need to get the standards and study them, then get mentored really.
There are various commercial machinery safety courses, mine was the CMSE validated by TUV Nord.

Please don't "play" with this stuff, because people die in and around machinery and there was a recent case where a machine designer has I think done time, if not certainly been found guilty of manslaughter because his design was negligent.

What makes it worse is the actions of one of the parties involved resulted in the death of a family member, they basically burned to death, or suffered a heart attack due to the temperatures when they were trapped inside an oven.
So just like the guys pictured hugging on top of the burning wind turbine with no means of escape, he knew that he was going to die, and was just sat/stood there waiting to die.
Horrible, so just realise that machinery safety is not something to take lightly.
 

Reply to Emergency Stop circuit in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
433
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Fitted a lot of this sort of light recently, with all tests reporting back through central Dali controller(s).
2
Replies
15
Views
993
nicebutdim
N
Yes, probably overthinkig, thanks.
Replies
6
Views
612

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top