OP
Deleted member 26818
Yes R1+R2.Surely that gives you r1 / r2 not end to end of the CPC ?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss End to end testing on cpcs ring circuit. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Yes R1+R2.Surely that gives you r1 / r2 not end to end of the CPC ?
It is normal to just measure the end to end at the CU. Although there is no reason why you can't measure the end to end at each accessory.
You would however expect each measurement to be the same.
From what you have described, it sounds as if you are not measuring end to end at each accessory, but between different conductors at each accessory.
Could you confirm exactly what you did please?:thumbsup
Are you just testing the CPC or have you interconnected with a Line or Neutral?
I'm probably being dense here but am I right in thinking you:
- joined the cpc connectors together in the cu and to nothing else.
- are breaking the ring at each socket in turn and measuring the continuity between the two cpc connectors.
- have checked there's nothing plugged into the ring or connected through a fsu.
Yep cpc connectors were jointed together in the consumer unit, in the main earth terminal.
When I did the test there would have been a fridge plugged in and a kettle, and there are 2 switched fuse units on the ring?
Would having things plugged in and having switched fuse spurs switched on affect the results of an end to end on the cpcs?
OK it sounds like you've got parallel paths there. You would need to make sure that nothing eles was connected to the cpc for the readings to be the same wherever you broke the ring.
Reply to End to end testing on cpcs ring circuit. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net