There does sound like a parralel path as spinlondon rightly said.
All the r1+r2 readings are equal within 0.05 at every outlet?

yeah all the reading are equal within 0.05 other than a spurred socket which you would expect to be higher.

i didnt understand what spinlondon said though, do you no what an interconnection is?
 
Disconnect the rfc cpcs from the cu and test from them to the MET this will tell you if there is a paralel path to earth on your circuit,
if you do then it may be a case of splitting the circuit at one outlet and testing each side and narrowing down the point of the parralel path.
without looking at it i cant really say what id do
 
Disconnect the rfc cpcs from the cu and test from them to the MET this will tell you if there is a paralel path to earth on your circuit,
if you do then it may be a case of splitting the circuit at one outlet and testing each side and narrowing down the point of the parralel path.
without looking at it i cant really say what id do

if it is a parrallel path it can only be from the aga which is connected to the ring circuit and the main bonding. are these parrallel paths a problem?
 
If there are two parallel paths (bonding to the aga and also to something else on the ring) then the cpc will effectively have an interconnection. You will therefore potentially have widely different readings at different points on the ring. Draw it out.
 
I have a Fluke manual that shows you step by step how to use your tester. I used to carry it in my tester box all the time just in case I couldn't remember teh exact procedure. PM me tomorrow and I will upload it for you, infact... I'll post it in a thread as I keep getting requests for it anyway:thumbsup

With everything unplugged and Fused Connection Units switched off...

Take the cpcs out of the consumer unit earth bar and test end to end what reading do you get?

After that reading, connect those two ends into a connector block (NOT CONSUMER UNIT EARTH BAR) and go to first socket and record reading, rejoin and go to next

Please take a note of all readings and post up here:thumbsup

Please be sure to be careful when using your tester, I'm all for learning but perhaps for the time being I wouls dtick to dead tests only... or at least until I have got this manual posted up;)
 
I have a Fluke manual that shows you step by step how to use your tester. I used to carry it in my tester box all the time just in case I couldn't remember teh exact procedure. PM me tomorrow and I will upload it for you, infact... I'll post it in a thread as I keep getting requests for it anyway:thumbsup

With everything unplugged and Fused Connection Units switched off...

Take the cpcs out of the consumer unit earth bar and test end to end what reading do you get?

After that reading, connect those two ends into a connector block (NOT CONSUMER UNIT EARTH BAR) and go to first socket and record reading, rejoin and go to next

Please take a note of all readings and post up here:thumbsup

Please be sure to be careful when using your tester, I'm all for learning but perhaps for the time being I wouls dtick to dead tests only... or at least until I have got this manual posted up;)


Thanks mate,

(Take the cpcs out of the consumer unit earth bar and test end to end what reading do you get?) i got 1.49 ohms and did throughout the circuit until the aga was connected then i started getting these varying reading unless i test from the consumer unit.
 
Had to read this a couple of times as your testing methods do not appear logical

If the Aga is feed via the spur your earth will be connected to the metalwork on it and if this is gas feed through metal pipework then your gas bonding will be one of your parellal paths. The values around the ring will vary as you will have a longer part of the ring in circuit
 

Reply to End to end testing on cpcs ring circuit. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
865

Similar threads

Well we called it a room, but it was only a hole in the ground covered with bit of canvas.
Replies
13
Views
640
Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top