Okay, so you've obtained your end to end results. What is it you are testing between at the sockets? are you still doing end to end or have you moved onto the next stage and using your figure of 8 (interconnected) LN LE NE. I'm afraid I'm missing something due to lack of information?
If you are still doing end to end on the cpc at each socket (not sure why) then what have you done with the cpc's that you did end to end on in the cu? Have you connected them in a connector block to complete the ring and enable you to test end to end at the socket outlets or have you terminated them back into the earth bar?
If there are FCU supplying a socket that these items are plugged into then just switch the FCU into the open position. This will eliminate the appliances.
Please tell us step by step exactly what you have done, it is only by doing this that someone can say "Ah ha, got it! that is what you are doing but you need to do this" or " sorry mate, you're Donald Duck'ed" lol
I'm reading this thread that you have done end to end on cpc's, put them back into the earth bar and then gone around testing for end to end continuity on the cpc at each socket outlet. If this is the case then I believe this is where you have made an error.
A step by step WILL help us HELP you.
Out of interest, what tester are you using?
:thumbsup
Thanks for the reply sorry if im not making myself very clear, im confusing myself and everybody else. ive used this website loads and valve everyone opinions. ok ill try again.
Ive obtained my end to end results from carrying out the tests in the consumer unit. I was just changing a socket on the same ring the other day and thought while the wires were loose ill do an end to end with the loose wires, everything else was still connected.
i was doing the end to end test at the socket just out of curiosity, the all the other cpcs including those in the consumer unit were connected in the existing sockets which then went back to the main earth terminal.
when i orginally carried out the end to end test before the dishwasher and aga were connected i was getting the above test results when carrying out the end to end tests in the consumer unit. im still getting the same results now with the aga and dishwasher connected when i do the end to end results at the consumer unit.
my only concern was when i did the end to end test just out of curiosity behind the socket my cpc results were not the same as what i was getting when i carried out the test in the consumer unit.
that is what i didnt understand, and the results were getting higher the closer i tested to the consumer.
i wasnt sure weather this could have been due to parrallel paths because when i did the end to end test behind the sockets the swtiched fuse spur was turned on which was supplying the aga, and the aga is connectedby gas which is main bonded.
your last point makes me think what i have been doing is clearly wrong.
i have done the end to end on the cpcs at the consumer unit, i have then put them back in the earth bar and tested the end to end for continuity at each socket outlet.
the tester im using is a fluke 1653
all my results on this ring circuit are,
l-l 0.90
n-n 0.92
r2-r2 1.49
r1+r2 0.67
insulation resistance all 500 meg
ze- 0.86 ohms
thanks again i hope this is a better explination.